Hi,
I was wondering if I need a GFCI plug for a fridge which stays by the side of the cabinets . There is about 2 ft of counter top between sink and fridge plug.


If I can , great, if not, what about this scenario:
Can I connect the fridge with same wiring that connect garbage disposal? Different GFCIs but the power comes from the box through the same wiring and then gets spliced between fridge and the disposal. Now there is a 15A circuit breaker. I plan to upgrade it to 20A.

Thx.


urimak is offline  
 
Reply With Quote
Old 05-19-2017, 06:04 PM  
Snoonyb
Senior Member
Join Date: Sep 2006
Posts: 2,415
Liked 423 Times on 375 Posts
Likes Given: 1

Default

If the recp for the refer is also accessible for any countertop appliances, then it must be GFCI protected.

A breaker protects the conductors so, if the conductors are #$14 than the max. breaker is the one there now.


__________________
Illigitimas non-carborundum
Snoonyb is offline  
2
People Like This 
Reply With Quote
Old 05-19-2017, 07:04 PM  
urimak
Junior Member
Join Date: Nov 2015
Posts: 4
Liked 1 Times on 1 Posts
Likes Given: 3

Default

Thank you. Much appreciated.
urimak is offline  
 
Reply With Quote
Old 05-19-2017, 09:45 PM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,369
Liked 2920 Times on 2560 Posts
Likes Given: 4808

Default

Quote:
Originally Posted by urimak View Post
Thank you. Much appreciated.
Do not change the breaker, the breaker is there to protect the wire and the 15 amp breaker is the limit for 14 g wire.
Just put up with the odd popped breaker, it might be worth a life of a loved one.
Motor in things like fridges don't like gfci because if they pop the fridge no longer runs and may be missed until it is two late.
Just change the outlet to a single plug so nothing else is used at that outlet.

See # 8201-4 on this page.
http://www.internationalconfig.com/c...ages/pg155.pdf
nealtw is online now  
urimak Likes This 
Reply With Quote
Old 05-20-2017, 08:20 AM  
Kabris
Senior Member
Join Date: Sep 2014
Posts: 187
Liked 42 Times on 36 Posts

Default

According to Code, all outlets in a damp location or within 6 feet of a sink basin shall be GFCI protected. However, I rarely put a refrigerator on a GFCI, mainly because they tend to nuisance trip over motor loads.

Technically a sump pump in a basement needs to be GFCI protected also. Personally that's something I wouldn't want to nuisance trip.
Kabris is offline  
joecaption Likes This 
Reply With Quote
Old 05-20-2017, 12:11 PM  
afjes_2016
Established Member
Join Date: Aug 2016
Location: , Northeast PA - USA
Posts: 252
Liked 112 Times on 92 Posts
Likes Given: 106

Default

Agree with others. Best is to replace duplex receptacle with a single 15amp receptacle where you have the fridge plugged into now. Does not have to be GFCI because there will only be one receptacle and it will be used only for the fridge. Totally code compliant-No. But if you know no one in the house will unplug the fridge and plug in something else then don't worry too much. The GFCI is for personal safety. If you go to sell your house then the inspector for the buyer may say something. Or just go and replace the receptacle with a GFCI receptacle but as stated GFCI don't really like motor loads that much, especially if it is an older fridge.

Do not upgrade a 15 amp breaker with a 20amp breaker. You are asking for problems in the future. If there is a 15amp breaker there now it means there is only 14 gauge conductors. Connecting the fridge to the disposal may present problems of over loading the circuit and tripping the breaker.

The other thing you may want to do is with the present fridge receptacle. Push the "Test" buttons on all the GFCIs that are in the kitchen now. Leave the fridge door open and see if when you press the test button if the fridge shuts off. This will answer your question. It may already be on a GFCI protected circuit that is connected to one of your small appliance circuits on the kitchen counter/s.


__________________

To the OP (O.riginal P.oster to this thread/topic).

If at any time you do not feel confident enough to perform a trouble shooting method that I suggest or feel you may not have the experience or comfort level to do so please ask questions before proceeding.
Electricity is dangerous and if not handled properly can cause serious injury or worse!
afjes_2016 is offline  
2
People Like This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Swapping non GFCI plugs for GFCI plugs swimmer_spe Electrical and Wiring 36 06-17-2016 02:44 PM
GFCI outlets vs GFCI breakers Dzarate29 Electrical and Wiring 6 11-01-2013 11:32 AM
24" sink base and undermount sink Question ggnuncleb Carpentry and Woodworking 0 07-16-2013 06:13 AM
oven/stove near fridge is making fridge warm. is this bad? what to do? adifrank Green Energy and Sustenance Living 9 10-16-2012 02:39 PM
fridge help handcock General Appliance Discussion 6 03-25-2008 10:07 AM



Newest Threads