Default Trane XE90 blower no longer spinning but making big noises

Blower will spin freely and smoothly when there is no power applied to it. I can watch the blower and it does want to spin in the correct direction but it is only crawling, like one degree every few seconds. Trying to push it by wooden stick shows lots of resistance as if there is a giant magnet holding it back. Start capacitor was replaced but that had no difference in the symptoms.

I checked the motor stator windings and they all checked out (4 - 6 ohms). I checked the voltage coming out of the controller when it commands the motor to spin. No load voltage is 120VAC and when the motor is making the noise, it is at 118VAC. I also tried all four leads and they all noises, some more some less.

When the motor spins freely without power, there is NO axial or lateral play. When the power is applied, I do not see any shift. This tells me that motor is mechanically sound. I am at a loss as to what can electrically go wrong with rotor on this type of motor. I am under impression that they are pretty much bulletproof.

I am concluding that I need new motor and motor only i.e. the fan assembly is fine (because it spins freely without power) and controller is fine (because it is providing 120VAC to the motor).

I would like to apply direct 120VAC to the motor but I do not like the unsafe aspect of it. Given that I have already measured the live voltage to the motor coming out of the controller at the junction and it is showing 120V, there is no logical reason to think applying direct wall power would make any difference. Can you come up with a scenario under which this assumption would be wrong?

As you can imagine, the house is very cold. I already had a technician come in and the motor is on the order. But I definitely want to make sure putting the new motor is going to fix it. I just can not take "oops, we need more parts and they need to be ordered" saga anymore.

Trane XE90 forced hot air, installed YR2000

Thanks,



__________________
vgs8606 is offline  
 
Reply With Quote Quick reply to this message
Old 01-22-2012, 05:40 PM  
paul52446m
Senior Member
 
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by vgs8606 View Post
Blower will spin freely and smoothly when there is no power applied to it. I can watch the blower and it does want to spin in the correct direction but it is only crawling, like one degree every few seconds. Trying to push it by wooden stick shows lots of resistance as if there is a giant magnet holding it back. Start capacitor was replaced but that had no difference in the symptoms.

I checked the motor stator windings and they all checked out (4 - 6 ohms). I checked the voltage coming out of the controller when it commands the motor to spin. No load voltage is 120VAC and when the motor is making the noise, it is at 118VAC. I also tried all four leads and they all noises, some more some less.

When the motor spins freely without power, there is NO axial or lateral play. When the power is applied, I do not see any shift. This tells me that motor is mechanically sound. I am at a loss as to what can electrically go wrong with rotor on this type of motor. I am under impression that they are pretty much bulletproof.

I am concluding that I need new motor and motor only i.e. the fan assembly is fine (because it spins freely without power) and controller is fine (because it is providing 120VAC to the motor).

I would like to apply direct 120VAC to the motor but I do not like the unsafe aspect of it. Given that I have already measured the live voltage to the motor coming out of the controller at the junction and it is showing 120V, there is no logical reason to think applying direct wall power would make any difference. Can you come up with a scenario under which this assumption would be wrong?

As you can imagine, the house is very cold. I already had a technician come in and the motor is on the order. But I definitely want to make sure putting the new motor is going to fix it. I just can not take "oops, we need more parts and they need to be ordered" saga anymore.

Trane XE90 forced hot air, installed YR2000

Thanks,
Can you spin the blower by hand when you have the power on it?
It sounds like it your Start capacitor is bad again. When you have them change the motor make sure you put a new capacitor to match the new motor. One other thing that can mess a motor up is, if for some reason two winding's of the motor get hotted up at the same time. Paul


__________________

Last edited by paul52446m; 01-22-2012 at 05:46 PM.
paul52446m is offline  
 
Reply With Quote Quick reply to this message
Old 01-22-2012, 05:56 PM  
vgs8606
Junior Member
 
Join Date: Jan 2012
Posts: 7
Default

The motor can not be spun by hand when the power is applied to it. As far as I can determine of the four spades coming out of motor, two are parked, one is for heat and the other is for cooling. Controller provides current to only one at a time.

I finally tred to hard-wire motor from the wall power and it does not want to spin. Something internal to the motor has gone bad.

__________________
vgs8606 is offline  
 
Reply With Quote Quick reply to this message
Old 01-23-2012, 07:15 PM  
vgs8606
Junior Member
 
Join Date: Jan 2012
Posts: 7
Default

Motor needed to be replaced. The new motor is quiet.

__________________
vgs8606 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Trane xe90 Blower Motor Not Kicking in Fitmiss HVAC 14 01-20-2012 09:35 PM
Trane xe90 Blower is running all the time skeatus HVAC 17 09-28-2011 06:35 PM
trane xe90 blower davidjackowiak HVAC 1 11-23-2010 02:52 PM
Trane XE90 Furnace Fan Always On Espritman HVAC 1 08-22-2009 06:52 PM
Trane XE90 TheGunMan HVAC 0 06-04-2009 05:53 PM

Newest Threads

LATEST SPONSOR DEALS