Default Intermittent pressure switch problem

Here's my problem. York Diamond furnace, heat turns on but after running for a while, turns off with 6 flashes indicating pressure switch opened 5 times after normal operation. Here are some observations.

1. Pressure switch is about 2 years old.
2. The tube from draft inducer to the pressure switch is clean.
3. The pressure from the draft inducer to the pressure switch seems low.
4. I can hear the draft inducer running and it sounds pretty strong.

so I'm thinking either one of these.

1. Bad pressure switch
2. Bad draft inducer
3. Clogged vent.

My questions are as follows:
1. How much suction should I expect from the draft inducer to the pressure switch? I feel some suction coming from the inducer when it's on but it's not so strong. Should it be really strong like it's sucking air strong or should it be slight?
2. How do I verify if I have a clogged vent??

Your help is appreciated. Thank you!

Joe


homeowner123 is offline  
 
Reply With Quote
Old 11-03-2012, 12:57 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

1. How much suction should I expect from the draft inducer to the pressure switch?
>What are your pressure switch spec's?

Should it be really strong like it's sucking air strong or should it be slight?
>You may be able to feel 0.5 PSI (14" of water column?). You can test this - fill a soda straw with water, block the top opening and see if you feel the pull of this many inches of water.

2. How do I verify if I have a clogged vent??
>Pressurize it, measure static pressure with a homemade manometer and compare the inches of WC with what is normal back pressure for a vent.

Last edited by Wuzzat?; 11-03-2012 at 01:12 PM.
Wuzzat? is offline  
 
Reply With Quote
Old 11-03-2012, 06:45 PM  
homeowner123
Junior Member
Join Date: Nov 2012
Posts: 2
Default

Quote:
Originally Posted by Wuzzat? View Post
1. How much suction should I expect from the draft inducer to the pressure switch?
>What are your pressure switch spec's?

Should it be really strong like it's sucking air strong or should it be slight?
>You may be able to feel 0.5 PSI (14" of water column?). You can test this - fill a soda straw with water, block the top opening and see if you feel the pull of this many inches of water.

2. How do I verify if I have a clogged vent??
>Pressurize it, measure static pressure with a homemade manometer and compare the inches of WC with what is normal back pressure for a vent.
Thanks for your response. The pressure switchis rated at 0.5" w/c. I guess thats really slight. I also checked the vent and there was no obstruction. I will try a new pressure switch and report back.
Joe
homeowner123 is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Trane XE 90 pressure switch eddie HVAC 70 12-17-2013 06:14 PM