In my kitchen I have the left side of the counter plugs on a 20 amp circuit, the right side on a 20 amp, and the center by the sink on a 20 amp circuit. The fridge and microwave are on a 20 amp circuit also. Last week I had too many items plugged into the left side circuit and it blew the breaker for it. However when I came back after resetting the breaker, the microwave needed reset and my wife said that it turned off and back on real quick when the breaker blew on her. The kitchen and fridge plugs are on different phases in the panel. I have the neutral and ground for the kitchen left side on the ground buss bar and the fridge and microwave neutral and ground are on the neutral buss bar. Anyone know why this is. I rewired everything else in the house because of knob and tube. Everything from new light fixtures, adding dedicated circuits, and putting in new plugs and switches and running all romex lines.



Last edited by ajr4997378; 11-28-2012 at 03:37 PM.
ajr4997378 is offline  
 
Reply With Quote
Old 11-28-2012, 05:16 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
registry_dropdown_4883_80579
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,326
Liked 145 Times on 123 Posts
Likes Given: 71

Default

That's just the way they wired it. As long as this is a properly installed "Main" panel, it will not make a difference.


kok328 is offline  
 
Reply With Quote
Old 11-28-2012, 06:02 PM  
ajr4997378
Junior Member
registry_dropdown_29434_80582
 
Join Date: Nov 2012
Posts: 25
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by kok328
That's just the way they wired it. As long as this is a properly installed "Main" panel, it will not make a difference.
I had an electrician do the service for the new panel. I added all of the circuits to it after that. I'm just wondering why the microwave and fridge would lose power for a second and come back on when the kitchen breaker would trip
ajr4997378 is offline  
 
Reply With Quote
Old 11-28-2012, 06:18 PM  
nealtw
Contractor
registry_dropdown_20526_80583
 
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,171
Liked 1304 Times on 1147 Posts
Likes Given: 2201

Default

Perhaps you have these two circuits together in a three wire and have the breakers tied together
nealtw is offline  
 
Reply With Quote
Old 11-28-2012, 06:37 PM  
ajr4997378
Junior Member
registry_dropdown_29434_80585
 
Join Date: Nov 2012
Posts: 25
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by nealtw
Perhaps you have these two circuits together in a three wire and have the breakers tied together
No I ran 2 separate 12-2 lines for these circuits and they are on single 20 amp GE breakers. I'm saying the fridge and microwave turn off for a split second every time the kitchen breaker trips.
ajr4997378 is offline  
 
Reply With Quote
Old 11-29-2012, 02:01 AM  
nealtw
Contractor
registry_dropdown_20526_80595
 
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,171
Liked 1304 Times on 1147 Posts
Likes Given: 2201

Default

Yup, that's a good question?
nealtw is offline  
 
Reply With Quote
Old 11-29-2012, 04:32 AM  
ajr4997378
Junior Member
registry_dropdown_29434_80597
 
Join Date: Nov 2012
Posts: 25
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by nealtw
Yup, that's a good question?
I can't figure it out either. I don't even have the neutral and ground for either of these circuits anywhere close to each other in the panel. I have the neutral and ground for the kitchen on the ground buss bar and the fridge and microwave neutral and ground on the neutral buss bar. When any other circuit trips in the house, I don't have any problems. I'm completely puzzled about this.
ajr4997378 is offline  
 
Reply With Quote
Old 11-29-2012, 05:06 AM  
inspectorD
Housebroken
HRT_ADMIN.png
 
inspectorD's Avatar
registry_dropdown_391_80598
 
Join Date: Dec 2005
Location: Litchfield, CT
Posts: 4,242
Liked 180 Times on 151 Posts
Likes Given: 448

Default hmm

Check all the box connections, make sure they are tight. Turn off the power first.
Also check the breakers, one may not be in fully.
Good luck.
__________________
Just My
Made in the
inspectorD is offline  
 
Reply With Quote
Old 11-29-2012, 08:52 AM  
Wuzzat?
Banned
registry_dropdown_17632_80602
 
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

If you can reproduce the symptom you have a chance of finding the cause.
Wuzzat? is offline  
 
Reply With Quote
Old 11-29-2012, 01:45 PM  
nealtw
Contractor
registry_dropdown_20526_80619
 
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,171
Liked 1304 Times on 1147 Posts
Likes Given: 2201

Default

I went reading about harmonics. And I am still guessing but if the first breaker kicks off it can change the wave and the computer in the microwave looses the top of the wave will reset but never lost power???
http://support.fluke.com/find-sales/...03_ENG_K_W.PDF


nealtw is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Mysterious Leak FreshFish Plumbing Forum 6 04-04-2012 03:36 PM
Mysterious smell Seaside Walls and Ceilings 2 12-23-2011 08:38 AM
Mysterious lost water pressure univox68 Plumbing Forum 5 09-11-2011 07:22 PM
Problem With Elec. Ceiling Heat kymike HVAC 1 12-13-2010 03:39 PM
Mysterious bulges in wall jrsharp21 Walls and Ceilings 6 07-12-2007 09:33 AM

Newest Threads

LATEST SPONSOR DEALS