Default hot water at pressure 125 - what does this say about 13yr hot water heater

Hi all,

I have a tanked hot water heater, 13 years old, that I am thinking is reaching the end of it's useful life, but wanted to get some expert opinion before replacing.

Current problem we are seeing
Hot water is venting via a wilkins 1500 valve (graduated screw in type) from the hot water side of the tank, to a pvc pipe and then to outside. It's been doing this for a number of weeks. Currently the wilkins valve is set to 125.

Note that this wilkins is inline with the hot water pipe exiting the tank and is separate from the TPR valve on the side of the tank. I don't know why I have this extra valve. I operated the TPR valve and it is working; vents when I pull it and stops when I release it.

Anyways, since the wilkins is set to 125, is that a high or low pressure for hot water or do I have room to play to alter it to stop this venting? (perhaps dangerous given it's a safety valve).

And what does this venting and the 125 value say about the health of the hot water heater?

Note that we don't have any complaints about the temperature or pressure of hot water into the house.

hot water heater details
50 gallon, tanked
model : PR6 5C NPRT971
State Industries Inc, Ashland City, TN
Original water heater install on new home 1999.

Thanks
mike



__________________
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2013, 03:20 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 991
Liked 109 Times on 89 Posts
Likes Given: 4

Default

put an actual pressure gauge on the system and see what the actual pressure is. Maybe the valve is failing.



__________________
JoeD is online now  
 
Reply With Quote Quick reply to this message
Old 04-21-2013, 06:23 PM  
montag
Junior Member
 
Join Date: Sep 2012
Posts: 19
Default

Quote:
Originally Posted by JoeD View Post
put an actual pressure gauge on the system and see what the actual pressure is. Maybe the valve is failing.
Do you mean measure the hot water pressure. How would I that since I am only familiar with the pressure gauges that fit on an outside faucet for the cold water. I guess I could cut in and add a suitable connector to one of the hot water pipes and measure from that.
__________________
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2013, 09:40 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,980
Liked 964 Times on 857 Posts
Likes Given: 1650

Default

that type of gauge would work on the tap for the washing machine.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2013, 10:38 PM  
montag
Junior Member
 
Join Date: Sep 2012
Posts: 19
Default

Quote:
Originally Posted by nealtw View Post
that type of gauge would work on the tap for the washing machine.
That's a great tip. I didn't think of the washing machine connection . Thank you. Just need to a gauge now from hd or lowes.
__________________
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2013, 11:20 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 991
Liked 109 Times on 89 Posts
Likes Given: 4

Default

The cold water should also be at the same pressure. Everything on the system should be at the same pressure. I suspect a failing valve or the TPR would be releasing also.

__________________
JoeD is online now  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 04-22-2013, 08:59 AM  
montag
Junior Member
 
Join Date: Sep 2012
Posts: 19
Default

Quote:
Originally Posted by JoeD View Post
The cold water should also be at the same pressure. Everything on the system should be at the same pressure. I suspect a failing valve or the TPR would be releasing also.
Thank you JoeD. I'll check the pressure on both hot and cold and post the results.
__________________
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-22-2013, 03:47 PM  
montag
Junior Member
 
Join Date: Sep 2012
Posts: 19
Default

I got a basic water pressure test gauge from Lowes (orbit model #91130) and tested both the hot and cold lines for pressure.

With no faucets on or any other items drawing water, cold is at 98psi and hot (or not so hot since its not really running at the time of test), at little over 100psi. So not good.

Could it be my Pressure Regulator Valve is faulty and not stepping down the pressure from the street? I should also have mentioned that when we have two faucets on at the same time and we get a wining sound from the plumbing. It doesn't bang, just a whine, medium pitch.

I plan to get a second, better test gauge later this week since I don't think I should rely on one test and one gauge. Will get something more robust from a professional plumbers supply place - just can't get there today with work etc.

As for my location, and I only mention this because the Lowes guy asked, am located in Cobb County, suburb of Atlanta and Lowes guy said my pressure should be around 45-50 something.

__________________

Last edited by montag; 04-22-2013 at 05:35 PM.
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-22-2013, 04:54 PM  
montag
Junior Member
 
Join Date: Sep 2012
Posts: 19
Default

Some additional info from my testing.

With the test gauge attached to the cold line it reads 98psi with no faucets or water being drawn. If I turn on a faucet on the same floor as the gauge, the pressure drops to 40psi. Then turn off the faucet and the pressure climbs back to 98psi and takes about 30-60 seconds.

__________________
montag is offline  
 
Reply With Quote Quick reply to this message
Old 04-22-2013, 05:09 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,980
Liked 964 Times on 857 Posts
Likes Given: 1650

Default

If you have a pressure reducing valve near the shut off valve you can take that down to about 60lbs and I think Joe is right about replacing the pressure release valve on the water tank.



__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
hot water heater - hot water venting outside from mixer valve montag Plumbing Forum 13 10-01-2012 04:21 PM
whole-house water filetration system and water pressure ilyaz Water Softener and Heater 7 07-31-2012 10:03 AM
Hot water heater not making hot water planehopr Plumbing Forum 1 02-23-2012 02:02 AM
MUST I replace a hot water heater that got water damage from Hurricane Irene? Seidperson Plumbing Forum 2 09-12-2011 08:12 PM
can I reuse hot/cold water flex lines on gas water heater? gordon Plumbing Forum 2 12-14-2008 01:16 PM

Newest Threads

LATEST SPONSOR DEALS