Default Siding wasn't primed before installation

A contractor just replaced some siding for me by my back steps. I'm about to paint the whole exterior of the house, including the new siding, but the new stuff wasn't even pre-primed before installation and is now between stairs and flashing, and completely inaccessible.

Besides getting them to rip it out, and then prime and paint before installation, any suggestions on what to do?

Should I caulk along the top side of the flashing? Will that unprimed siding below the flashing just rot out quickly? (I'm in a wet area, that's the north side of the house).

Thanks.

Above:



Below:



__________________
northbay is offline  
 
Reply With Quote Quick reply to this message
Old 09-14-2013, 11:43 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 11,060
Liked 997 Times on 882 Posts
Likes Given: 1664

Default

Not sure what he was trying to do with this flashing. The first board on the deck should have been removed and the flashing should be behind the house wrap and over the rim joist. Replace the deck board and the siding stops just above the deck. This pictureshows the siding behind the deck board but painting the siding becomes impossible.



deck flashing.jpg  
__________________

Last edited by nealtw; 09-14-2013 at 11:45 AM.
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 09-14-2013, 12:03 PM  
northbay
Junior Member
 
Join Date: Sep 2013
Posts: 2
Likes Given: 1

Default

Right, I think flashing was also installed behind the siding and wrap — over the rim joist — but then this extra piece on the outside too. The ledger for these stairs is away from the siding with spacers.

But, given this situation, is there any way that I can prime and paint this adequately, because there's always going to be bare siding behind that flashing.

__________________
northbay is offline  
 
Reply With Quote Quick reply to this message
Old 09-14-2013, 12:17 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 11,060
Liked 997 Times on 882 Posts
Likes Given: 1664

Default

If the upper flashing was done correctly it would be vissible above the rim joist in the second photo.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 09-15-2013, 07:51 AM  
GBR
Senior Member
 
Join Date: Mar 2009
Posts: 348
Liked 23 Times on 22 Posts
Likes Given: 9

Default

I agree with Neal. It is flashed wrong as the nails/flashing top edge are visible on top the T1-11 siding instead of underneath it in the first pic. Water will run down the grooves in the siding and rot it very quickly as no air movement to dry and flashing at bottom of ledger will collect it there. Capillarity/gravity will keep the bottom of the structural sheathing wet/damp and rot for sure because of cover. Add more lag screws per Table in here; http://www.awc.org/Publications/DCA/DCA6/DCA6-09.pdf.

It appears they flashed the siding without removing/reinstalling the first two deck boards; lame- it is guaranteed to leak. Lack of paint is the least of your concerns.... also pull one of the diagonal nails in any hanger- they should be 3" long; minimum; 2x6- LUS- into joist; http://www.strongtie.com/products/co...ce_ss-df1.asp# If those are indeed labeled (LUS).

Gary

__________________

Last edited by GBR; 09-15-2013 at 07:52 AM. Reason: sp
GBR is offline  
 
Reply With Quote Quick reply to this message
Old 09-15-2013, 11:56 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 11,060
Liked 997 Times on 882 Posts
Likes Given: 1664

Default

The fix here is to remove thye siding and a few deck board add the right flashing and cut the siding to fit.



__________________
nealtw is offline  
northbay Likes This 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Seeking Advice - Improper Installation of Vinyl Siding archenil General Home Improvement Discussion 5 08-18-2013 07:42 PM
Is siding with contoured foam siding needed if going over asbestos based shingles? sportsduck Roofing and Siding 3 05-14-2012 11:01 AM
Central AC wasn't working, now suddenly is. jbooth42 HVAC 0 09-21-2011 08:37 PM
New Disposal Installation jkirby65 General Appliance Discussion 5 07-22-2008 10:43 AM

Newest Threads

LATEST SPONSOR DEALS