DIY Home Improvement, Remodeling & Repair Forum > DIY Home Improvement > Electrical and Wiring > Voltage not adding up




Reply
 
Thread Tools Search this Thread Display Modes
Old 10-14-2013, 07:07 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,347
Liked 148 Times on 126 Posts
Likes Given: 71

Default

Cable 1, open neutral
Cable 2, open hot
Cable 3, open hot


kok328 is offline  
 
Reply With Quote
Old 10-14-2013, 09:12 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 2,007
Liked 634 Times on 490 Posts
Likes Given: 237

Default

Taking the switch out was a good idea and isolating everything. As you would think the two loads won’t have anything on them cable 2 and 3. You should measure 120 v from black to white and from black to ground on cable 1. The black wire is the hot wire and the common is white. You shouldn’t be getting voltage readings of anything except zero and 120 so these 20 and 70 volt readings are not right.

What type of meter are you using and on what setting on the meter?

If those readings are correct you have to chase the problem back down that cable to where it comes from. If you have anything you can use as a test load like a light bulb and do it safely you could test at each set of wires and see what the bulb does. If you have the low voltage you say you will see a very dim light at the low voltage. I keep a refrigerator socket with a rough service bulb in my meter box with a set of test leads attached and it’s quite handy for stuff like this.

Likewise I have a power lead that’s fused that I can plug into a good circuit and power up something like your fan cable just to make sure those cables are working the way they should.


bud16415 is offline  
 
Reply With Quote
Old 10-14-2013, 11:47 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,347
Liked 148 Times on 126 Posts
Likes Given: 71

Default

Bud, on a switch leg with the switch removed, you will have 0 volts between black & white, white & ground, black & ground.
kok328 is offline  
 
Reply With Quote
Old 10-14-2013, 01:08 PM  
bud16415
Fixer Upper
 
bud16415's Avatar
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 2,007
Liked 634 Times on 490 Posts
Likes Given: 237

Default

From his last post he said he had 3 cables coming into the box number 1 was the power for the circuit and 2&3 were loads one being a fan of some kind and the other an outlet box or something like that. If you remove the switch I was saying the feed into the box cable one would have power to it. It sounded like the power then went straight to the outlet and thru a switch to the fan. That was my take on it anyway. Taking the switch out should leave everything down stream dead.

The other method would be having the power originate at the device and then come to the box to be switched it didn’t fit his scenario as well I thought.

He didn’t mention odd voltages around the rest of the house. Or things not working just this one circuit. Strange voltages make me thing of a missing ground also. Maybe I totally misread his problem I will have to go back and read it from the beginning. I started where he said don’t pay any attention to all the above.
bud16415 is offline  
 
Reply With Quote
Old 10-14-2013, 01:18 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,347
Liked 148 Times on 126 Posts
Likes Given: 71

Default

missing ground shouldn't cause low voltage problems. At this point, the OP has us all confused.
kok328 is offline  
 
Reply With Quote
Old 10-14-2013, 05:34 PM  
JoeD
Contractor
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 1,096
Liked 138 Times on 112 Posts
Likes Given: 4

Default

Like I said back in post #4 and #9 you have an open neutral on the supply cable.


JoeD is offline  
nealtw Likes This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Doorbell voltage? drewdin Electrical and Wiring 7 01-04-2013 04:27 PM
Low voltage transformer? sdupp Electrical and Wiring 8 02-01-2012 06:28 AM
low voltage garbert Electrical and Wiring 1 11-13-2011 12:16 PM
Adding Dimmers- It's warm and how to determine if I have low voltage lights Cameoway Electrical and Wiring 1 08-01-2010 06:57 AM
Low Voltage Coqui Introductions 1 07-22-2006 05:01 PM

Newest Threads

LATEST SPONSOR DEALS