Default 12/2 Romex or 14/2 Romex for Recessed Can Lighting?

I'm installing 6 can lights in my kitchen and I bought 12/2 Romex for the wiring, a friend said I need 14/2 Romex, will 12/2 work or do I need to spend the money and get 14/2?





__________________
savatreatabvr is offline  
 
Reply With Quote Quick reply to this message
Old 01-05-2014, 05:50 PM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,343
Liked 400 Times on 312 Posts
Likes Given: 130

Default

12-2 will work fine. Number 12 is a little harder to work with and costs more. Other than that it's fine even better than 14.



__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 01-05-2014, 06:08 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Are you adding to a circuit or wiring a new circuit?
If you are adding to an existing you must stay with the size of the circuit.
Either way I'd return the 12 and get the 14. MUCH easier to work with in those boxes.

And your friend was wrong, they don't have to be on #14 and a 15A circuit, but they can. Unless you're in Canada, I believe up there lighting must be on 15A circuits.

Have you done any wiring before?

__________________
speedy petey is offline  
drewdin Likes This 
Reply With Quote Quick reply to this message
Old 01-05-2014, 07:56 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 985
Liked 108 Times on 88 Posts
Likes Given: 4

Default

Yes in Canada lighting is limited to 15 amp circuits.
The circuit breaker for the circuit determines the wire needed. If the circuit is 20 amp then you must use use the #12 cable. If the circuit is 15 amp then you can use #14 or #12 although #12 is a waste of money and harder to work with.

__________________

Last edited by JoeD; 01-06-2014 at 09:39 AM.
JoeD is offline  
speedy petey Likes This 
Reply With Quote Quick reply to this message
Old 01-06-2014, 09:41 AM  
savatreatabvr
Member
 
Join Date: Oct 2013
Posts: 46
Liked 7 Times on 5 Posts
Likes Given: 1

Default

Quote:
Originally Posted by speedy petey View Post
Are you adding to a circuit or wiring a new circuit?
If you are adding to an existing you must stay with the size of the circuit.
Either way I'd return the 12 and get the 14. MUCH easier to work with in those boxes.

And your friend was wrong, they don't have to be on #14 and a 15A circuit, but they can. Unless you're in Canada, I believe up there lighting must be on 15A circuits.

Have you done any wiring before?
Yes, I install commercial/residential security, fire, access control and CCTV systems but normally it's only 12vdc to 24vac max. We sub out the 120vac that powers our panels so as MORONIC as it sounds I've never really made it a point to learn 120vac wiring. Another issue I'm having is I hired a couple laborers from HD parking lot, (big mistake) but it never crossed my mind to have them ID the cables once they ripped out the appliances and lighting so now I've got several mystery cables that I have no idea were they go. Is there an easy way to ID these cables without ripping out drywall to see where they go?
__________________
savatreatabvr is offline  
 
Reply With Quote Quick reply to this message
Old 01-06-2014, 10:02 PM  
savatreatabvr
Member
 
Join Date: Oct 2013
Posts: 46
Liked 7 Times on 5 Posts
Likes Given: 1

Default

Quote:
Originally Posted by speedy petey View Post
Are you adding to a circuit or wiring a new circuit?
If you are adding to an existing you must stay with the size of the circuit.
Either way I'd return the 12 and get the 14. MUCH easier to work with in those boxes.

And your friend was wrong, they don't have to be on #14 and a 15A circuit, but they can. Unless you're in Canada, I believe up there lighting must be on 15A circuits.

Have you done any wiring before?
I'm basically deleting one ceiling light and replacing it with 6 can lights throughout the kitchen ceiling. Since I didn't demo the cabinets I'm not sure where the power for the original ceiling light comes in at, there are several unidentified cables that seem to disappear in the ceiling/floor, (2 story house) so I'm not sure how to power the new can lights now. Is it possible to get power from a kitchen outlet without overloading the circuit?
__________________
savatreatabvr is offline  
 
Reply With Quote Quick reply to this message
Old 01-07-2014, 09:15 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,343
Liked 400 Times on 312 Posts
Likes Given: 130

Default

I would think the first step is to figure out what those existing cables are and what you are going to do with them. You can’t just leave live feeds in the ceiling joists. First step is to figure out what breaker they are on and then figure out what switch if any controlled them. You could reuse them even if they will reach your first light. If not you need to kill power to them at some junction box. I would suggest breaking the 6 cans up on 2 or 3 switches. I just did something similar on my remodel the center light location became a ceiling fan and light unit and then I added 4 can fixtures. I put the fan on one switch and the fan light another and then 2 cans on one switch and two on another. We found that highly desirable as we often just need light on one end of the kitchen or the other. I added one more hanging light above the sink with its own switch. The one thing I didn’t do that I wish I had was wire at least one of the lights as a 3 way switch, we normally control all the lights as we come in from outside and all the switches are located there. But at night it would be nice to not have to walk across the dark kitchen to the far side. I did leave a wire unused in the wall from that side of the room to above an upper cabinet with the plan of adding an up light for just this reason. Really glad now I have that wire ready to go. Take your time planning because you will never have good access to that area again most likely.

__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 01-09-2014, 07:50 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Quote:
Originally Posted by savatreatabvr View Post
IAnother issue I'm having is I hired a couple laborers from HD parking lot, (big mistake) but it never crossed my mind to have them ID the cables once they ripped out the appliances and lighting so now I've got several mystery cables that I have no idea were they go.
Quote:
Originally Posted by savatreatabvr View Post
I'm basically deleting one ceiling light and replacing it with 6 can lights throughout the kitchen ceiling. Since I didn't demo the cabinets I'm not sure where the power for the original ceiling light comes in at, there are several unidentified cables that seem to disappear in the ceiling/floor, (2 story house) so I'm not sure how to power the new can lights now. Is it possible to get power from a kitchen outlet without overloading the circuit?
WOW! You actually hired men off the parking lot at HD to do this???

Unless you are really good at electrical troubleshooting, at this point my only advice is to bite the bullet and hire a pro. It might really bother you to pay a professional for a well earned day's work, but sometimes you have to do it.
__________________
speedy petey is offline  
kok328 Likes This 
Reply With Quote Quick reply to this message
Old 01-11-2014, 07:16 PM  
savatreatabvr
Member
 
Join Date: Oct 2013
Posts: 46
Liked 7 Times on 5 Posts
Likes Given: 1

Default

Quote:
Originally Posted by speedy petey View Post
WOW! You actually hired men off the parking lot at HD to do this???

Unless you are really good at electrical troubleshooting, at this point my only advice is to bite the bullet and hire a pro. It might really bother you to pay a professional for a well earned day's work, but sometimes you have to do it.

Some of us don't make as much money as you do so I'd rather do it myself and hire "men off the parking lot at HD" then hire an over priced arrogant pro that MILKS his time and charges for every single wire nut!!!
__________________
savatreatabvr is offline  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 01-12-2014, 08:01 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Quote:
Originally Posted by savatreatabvr View Post
Some of us don't make as much money as you do so I'd rather do it myself and hire "men off the parking lot at HD" then hire an over priced arrogant pro that MILKS his time and charges for every single wire nut!!!
Well, I don't make as much as you might think, which is why I DIY pretty much everything in my home.
And what makes you think that EVERY professional tradesman is A) arrogant, and B) "MILKS" his time on a job??? Have you fallen victim to a shady fly-by-night contractor? If so I am sorry. There are unfortunately plenty of them out there to give us legitimate honest guys a bad name. This is why you should always go by recommendations and word-of-mouth.

Also, WHY would we not charge for every wire nut???? I paid for them, I use them on your job, WHY would I give them away for free??????
What do you do for a living? Is it customary that you give things away? Or work some of your time for free?
Every been to a layer, or an accountant, or Target?? Not many freebies there either.


__________________
speedy petey is offline  
3
People Like This 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Outdoor THHN transition to Indoor Romex toofast Electrical and Wiring 6 10-17-2013 02:27 PM
Romex Vs THHN in condtioned area gottodo1 Electrical and Wiring 10 08-24-2013 12:26 PM
Nm-b romex run outdoors alexb5647 Electrical and Wiring 24 03-11-2013 11:17 AM
connecting old BX cable to new romex wiring drewdin Electrical and Wiring 6 01-02-2013 01:01 PM
Romex Routing in Attic 69-er Electrical and Wiring 3 02-19-2007 03:40 PM

Newest Threads

LATEST SPONSOR DEALS