Default Tacos, BGs & baseboard oh my

One of my zones isn't circulating. Was fine a few days ago (zone not used constantly), been in service for 6 years.

Being somewhat ignorant I replaced the cartridge in the Taco 007. no change. disassembled it again and tested power to the impeller. aok. re-assembled.

Argo control board lights properly when the tstat calls, taco works. what the 'ell else can it be? Ahhh what about that red thing over there?

yes being somewhat ingnorant i thought the red thing was on the return -- not the supply. (esp since the tacos are warm/hot and that is not. I found a doc at Xylem/BG site for the flo contorl valve sa1 3/4 it shows an exploded parts diagram and talks about cleaning.

Does blockage/failure of the valve seem to be the culprit?
It certainly seems so -- no leaks anywhere, working ok a few days ago. Not a complicated installation -- But I don't have isolators on both sides of the valve -- so I'll have to drain -- not fun in the winter.

Anybody know why it would require cleaning? or have any pointers on the process? thanks, bryan


rokosz is offline  
 
Reply With Quote
Old 01-15-2014, 03:11 PM  
rokosz
Member
Join Date: Jun 2013
Posts: 41
Liked 10 Times on 9 Posts
Likes Given: 7

Default

For all time, let it be known here:

A simple hammer (tap(ping)) on the illustrious BG Flo-control solved the circulation issue.

It kind of solved itself too-- I'd shut all the isolators (3 --2 @ return, one into the BG). Called for service. Open the balls, hit the stat -- and flow gently down the stream. Tech explained they usually give a shot or two with a hammer to the BG.

I'd begun the attempt to "rebuild" or at least clean out the valve -- but didn't like tugging on all that copper and stopped without even beginning to loosen the packing nut or plug. Tech poo-pooed attempting any removal of the plug or valve assembly.

I'd also tried turning the valve control open and closed a few times prior to isolating the zone.

so combo of isolation and valve or one or the other? Next time I'll try tapping it


rokosz is offline  
inspectorD Likes This 
Reply With Quote
Old 01-15-2014, 08:35 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,495
Liked 1344 Times on 1185 Posts
Likes Given: 2317

Default

Sorry you didn't get any help here, thanks for the update.
nealtw is offline  
 
Reply With Quote
Old 01-16-2014, 07:28 PM  
inspectorD
Housebroken
HRT_ADMIN.png
 
inspectorD's Avatar
Join Date: Dec 2005
Location: Litchfield, CT
Posts: 4,255
Liked 186 Times on 155 Posts
Likes Given: 462

Default Yes

Thanks for the Update!! It's good to learn something new.I mean, who knew you just needed a hammer to fix your parts....usually ends up with extra parts.
__________________
Just My
Made in the
inspectorD is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Baseboard Transition dzuroff Walls and Ceilings 2 03-31-2011 12:26 PM
Help with wall behind baseboard Hurryheathen General Home Improvement Discussion 4 10-17-2010 03:31 PM
Insulation behind baseboard? Razztjazz Insulation and Radiant Barriers 1 07-07-2010 05:48 AM
Baseboard question jeiowa01 Flooring 1 07-10-2009 09:46 PM
One HOT baseboard! MarkBrown HVAC 1 01-07-2008 05:25 PM

Newest Threads

hey

LATEST SPONSOR DEALS