Last night me and the wife where whatching tv in the living room. Out of nowhere the living room started erratically cycling power about 3-4 times. (lights, ceiling fan, tv, etc.) End result being my living room is now dead...

ALL other circuits (rooms) in my home where completly unaffected and are fine. It was only my living room experiencing the freak out.

I went straight to the panel. Breaker was not tripped, so I cycled it which was no fix... I took my digital multimeter and I had 120v out the breaker with it closed and none with it open as it should.

Checking a few outlets in my living room show 120v on both sides of the outlet. (hot to ground / neutral to ground)

I replaced all the wall plates when I first bought the home and I do have the screw down connections and NOT the push-lock style. I also pulled a few plates off last nigh and did not see any loose, broken or shorted connections.

I left the breaker off and I am at work now. When I get home I will follow the hot wire from the breaker to the bundle in the panel and see from the bundle where the nuetral is connected to the panels block. Hopefully it will be there. A quick once over last night did not show anything obvious.

Any ideas?



__________________
Joeb1983 is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 10:38 AM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 991
Liked 109 Times on 89 Posts
Likes Given: 4

Default

Your voltage readings are indicating an open neutral. It could be in the panel or any one of the device boxes on the circuit. If part of the circuit is still working it could be in a working box as well. If you know the route the cabling takes the problem is in the first not working box or last working box.
I would start by checking the box closest to the panel since cable usually run away from the panel.



__________________

Last edited by JoeD; 05-15-2014 at 10:41 AM.
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 10:45 AM  
Joeb1983
Junior Member
 
Join Date: May 2014
Posts: 5
Liked 1 Times on 1 Posts

Default

Yeah thats what I figured. When I get home I will start at the panel and work my way down the line. Hopefully it is something simple. Appreciate the reply!

__________________
Joeb1983 is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 02:46 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

The loads that are plugged in in your living room are why you are reading 120v on the open neutral.
With everything unplugged from that branch you may read 60v on the neutral with the reading depending on what kind of meter you have, the length of the branch wiring and if the cable has a ground conductor (which yours does). It's a Phantom Voltage.

If you find an appliance that operates normally on that branch, the open in the neutral is between the living room and that appliance.

__________________
Wuzzat? is offline  
CallMeVilla Likes This 
Reply With Quote Quick reply to this message
Old 05-15-2014, 05:51 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,980
Liked 964 Times on 857 Posts
Likes Given: 1650

Default

Quote:
Originally Posted by Wuzzat? View Post
The loads that are plugged in in your living room are why you are reading 120v on the open neutral.
With everything unplugged from that branch you may read 60v on the neutral with the reading depending on what kind of meter you have, the length of the branch wiring and if the cable has a ground conductor (which yours does). It's a Phantom Voltage.

If you find an appliance that operates normally on that branch, the open in the neutral is between the living room and that appliance.
He gets 120 on the neutral because a light or something is completing the loop
__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 08:25 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

Yes, the plugged-in loads are supplying the current to the multimeter. With nothing plugged in and an open neutral he should read a Phantom Voltage.

With a heavy load like a hair dryer instead of a multimeter, it should operate between hot and ground but hardly work between neutral and ground even though the open circuit voltage on each with respect to ground is similar. It's because the source resistance of the hot lead is about a half ohm but the source resistance of the open neutral through the loads is several ohms.

__________________

Last edited by Wuzzat?; 05-15-2014 at 08:28 PM.
Wuzzat? is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 09:21 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,980
Liked 964 Times on 857 Posts
Likes Given: 1650

Default

I know you love your multi meter, But let's get down to solving the problem. With the breaker turned on and with a light turned on at the other end of the run. If neutral is reading 120, the opening is closer to the breaker, if it reads close to zero it is further away. That is all you really have to know and on a bad day you find a bad wire between two boxes and open a wall to find where the squirles live and chew wires.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2014, 10:27 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,309
Liked 409 Times on 319 Posts
Likes Given: 171

Default

Can't wait to hear how this resolves ... dead mouse in the wall?

__________________
CallMeVilla is offline  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 05-16-2014, 08:35 AM  
Joeb1983
Junior Member
 
Join Date: May 2014
Posts: 5
Liked 1 Times on 1 Posts

Default

Alright guys found the issue yesterday after work. I took the cover off the panel and traced the hot (black) wire from the breaker to the romex bundle at the top; then followed the neutral (white) wire back down from that bundle to the panels neutral/ground block. Sure as anyhting the neutral wire was burnt up about 3" back from the tip. I was able to simply/easily pull it out of the block. I cut the "dead" stuff off, strip and reconnected to a new terminal lug. Good to go!

I heard the 60hz is a "slow pulse" and actually induces and slight vibration that over time will do exactly what happened... The house was built in 03. I know hospitals have a time complience/preventitive maintenance schedule to tighten them down ever so often. I did just that and tighten ALL my neutrals. To my surpise a few needed tightning.

Learn something everday! Thanks all!

__________________

Last edited by Joeb1983; 05-16-2014 at 08:49 AM.
Joeb1983 is offline  
CallMeVilla Likes This 
Reply With Quote Quick reply to this message
Old 05-16-2014, 08:40 AM  
Joeb1983
Junior Member
 
Join Date: May 2014
Posts: 5
Liked 1 Times on 1 Posts

Default

Oh and every outlet on that circuit was reading 120v on both when the problem was an issue. I unlugged everything from all the outlets on that circuit as well with the same readings; although my can lights and ceiling fan are also on that circuit. All other circuits in my home read 120v on hot, 0v on neutral and 120v between the two. Now the "problem" circuit reads as it should.



__________________

Last edited by Joeb1983; 05-16-2014 at 08:43 AM.
Joeb1983 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Garage door won't open all the way! dekor8r2008 Windows and Doors 35 07-14-2014 04:37 PM
What to do with open circuit gottodo1 Electrical and Wiring 8 02-13-2014 11:59 AM
Converting a staircase from open on 1 side, to open on 2 sides. frozensneaker Carpentry and Woodworking 5 11-17-2013 02:53 PM
Open Ground david542 Electrical and Wiring 12 03-07-2012 12:20 PM
i have an open ground.. mundo Electrical and Wiring 3 05-15-2011 08:35 AM

Newest Threads

LATEST SPONSOR DEALS