Default Running a heat duct down the inside of a wall

Just wondering what the standard approach is to running a new heat duct down the inside of wall.
The wall in question is 2x4 construction and is not funished but will be drywalled soon after the duct is installed.

Also would the same practice be applied to the return?



__________________
JoulesWinfield is offline  
 
Reply With Quote Quick reply to this message
Old 01-25-2007, 04:11 PM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

A 3" X 12" duct can be run in a wall but is limited in cfms to somewhere around 100 to 150, which will heat a small room (10' X 12'). If you need more than that you could run more than one duct. Return air can be run without duct.
Glenn



__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 01-26-2007, 06:13 AM  
JoulesWinfield
Member
 
Join Date: Dec 2006
Posts: 33
Default

So is the 3x12 duct something I can buy or would I need to bend it up myself?

Also since only one side will be drywalled for now should I just cover the other side with a peice of sheet metal?

__________________
JoulesWinfield is offline  
 
Reply With Quote Quick reply to this message
Old 01-26-2007, 01:16 PM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Oops. The standard size is 3-1/4" X 10" and it comes in 2' sections. It is made by Gary Steel Mfg. and should be for sale in your area at a Heating and Air Conditioning supply house. I would not worry about covering the back of it.
Glenn

__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 01-26-2007, 08:56 PM  
JoulesWinfield
Member
 
Join Date: Dec 2006
Posts: 33
Default

I was thinking there would be something like that. I found the piece that goes from the 6" duct between the joists and 90's into the wall. But I couldnt seem to find the actual duct that would extend down in the wall.

A friend of mine suggested just putting sheet metal on both sides and mounting the register on the drywall. That really didnt seem like the proper way to do it.

Ill have to check around to find the local supply house.

Thanks again Glenn.

__________________
JoulesWinfield is offline  
 
Reply With Quote Quick reply to this message
Old 01-26-2007, 09:14 PM  
Daryl
Member
 
Join Date: Sep 2005
Posts: 80
Default

THey also make an oval shaped ductwork for the supply line (one that delivers the heat to the room) which will fit in the confines of the 2X4 wall (it's looks like a squashed 6" round ) and comes in 6 ft lengths and is available at the local HD (lowes is very limited on this item in my area). They make the end stacks for the register too as well as the connection peices to 6" round. This allows you get the CFM rating higher than 100-150. Keep your 90 bends to a minimum as this cuts down on the airflow considerably. You can use the space between the studs for the return. Just cover the open side with sheet metal to allow the draw of the air on the return to the furnace.



__________________
Daryl is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Electric Heat Pump & Programmable Thermostat John Greeb HVAC 2 01-09-2009 10:01 PM
unequeal heat pump/air handler tonnage howie89 HVAC 6 06-19-2008 10:32 AM
Drill up, inside wall with least damage to wall? gfw Flooring 2 05-16-2008 05:01 PM
BIG retaining wall is on its way out mjordant Bricks, Masonry and Concrete 5 05-11-2008 06:10 PM
Thermostat line running through duct intake ITParalegal HVAC 4 09-10-2007 12:28 PM

Newest Threads

LATEST SPONSOR DEALS