About a year ago, I wired my attached garage with a subpanel. My sub in the garage is only 15 feet or so from the main. I used 4 AWG THHN 90C for both hots and netrual, 6 AWG bare stranded for the ground. The conductors are installed in 1.25" PVC 90C rated conduit.

The table I looked at when I bought the wire said #4 was good for 95A (w/90C insulation) My breakers are the Cutler-Hammer BR type. Since there was no 95A breaker avaliable, I used a 100A.

In hindsight, I'm wondering if using the 100 Amp BR this was the right thing to do? Should I switch it to a 90A breaker? The only reason I can think of to change it to 90A would be because of de-rating due to conduit fill. Can someone help me out?



TIA,
Mach1



__________________
Mach1 is offline  
 
Reply With Quote Quick reply to this message
Old 08-04-2007, 05:01 PM  
Parrothead
Member
 
Join Date: Dec 2006
Location: , WI
Posts: 65
Likes Given: 1

Default

Derating isn't an issue here, since there are only three current-carrying conductors in the pipe. However, the wire you used is only rated for 95 amps, and they are protected by a 100- amp breaker. to make it legal, you're going to either have to up-size the wire to #3 or down-size the breaker to 90 amp.

BTW, since this is a subpanel, did you make sure to remove the bonding jumper in the subpanel??? Just a thought.

__________________
Parrothead is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Tilson Home's cracked concrete garage stoker Bricks, Masonry and Concrete 16 07-25-2013 04:59 PM
good wiring reference? garage and loft. Philphine Electrical and Wiring 2 01-08-2009 07:55 PM
Overheating Garage wheelman General Home Improvement Discussion 14 12-20-2006 12:29 PM
Firewall questions on garage frank754 General Home Improvement Discussion 5 07-31-2006 08:22 PM
Cieling In Garage Addition Will Carpentry and Woodworking 10 06-24-2006 04:48 PM

Newest Threads

LATEST SPONSOR DEALS