Default number of can lights for a 20 amp breaker

I was wanting to put some recessed can lights in my entry and hallway for better lighting. I am considering the 4' Halo cans for remodeling. I was curious as to what the the recommended number of lights on a single circuit would be. I do not have a problem to put either a 15 or 20 amp breaker in and then running the new wire to the new lights. any help would be greatly apreciated.


adagaue37 is offline  
 
Reply With Quote
Old 03-12-2008, 03:01 PM  
speedy petey
Lic.Electrical Contractor
registry_dropdown_722_16878
 
Join Date: Mar 2006
Posts: 453
Liked 41 Times on 28 Posts
Likes Given: 17

Default

Use the actual rating of the cans, probably 75 watts for the 4", to figure wattage.
Use the 80% figure for the circuit load for lighting such as this.

20A@120v = 2400 watts x 80% = 1920 watts 75 watts = 25 fixtures
15A@120v = 1800 watts x 80% = 1440 watts 75 watts = 19 fixtures


speedy petey is offline  
 
Reply With Quote
Old 03-12-2008, 03:52 PM  
OtbHunter
Member
 
OtbHunter's Avatar
registry_dropdown_5558_16879
 
Join Date: Feb 2008
Posts: 35
Liked 1 Times on 1 Posts

Default

Wow, thanks for that explaination speedy petey. I didn't know that was how to figure how many lights on a breaker. Very good information to know!
__________________
Life Member = USA + NRA + USMC = Semper Fi
OtbHunter is offline  
 
Reply With Quote
Old 03-13-2008, 09:32 AM  
adagaue37
Junior Member
registry_dropdown_5957_16893
 
Join Date: Mar 2008
Posts: 5
Default thanks

Thanks Speedy Petey i really do appreciate the information. along the same lines if I use an existing run and it is not just lights but a mixture of lights and outlets what would the rule of thumb be on that. and if I use the fluorescent bulbs instead of the spot bulbs would you see a draw back to that? I am wanting to use the fluorescent replacements where I can to cut down on electrical usage and cost. currently 90% of the bulbs in my house are fluorescent bulbs.
adagaue37 is offline  
 
Reply With Quote
Old 03-13-2008, 02:31 PM  
speedy petey
Lic.Electrical Contractor
registry_dropdown_722_16894
 
Join Date: Mar 2006
Posts: 453
Liked 41 Times on 28 Posts
Likes Given: 17

Default

In a home there is no limit to the number of receptacles on a circuit. We just use common sense when figuring circuits.
I try to keep it to no more than 8-12 receptacles. If there is lighting I just compensate for it.
Using the CFLs is a good idea, just still use the actual wattage rating of the fixture when figuring circuits.
speedy petey is offline  
 
Reply With Quote
Old 11-20-2008, 11:16 AM  
trips
Junior Member
registry_dropdown_11169_25395
 
Join Date: Nov 2008
Posts: 1
Default Simplified Explanation

Basically your total amperage will equal your watts divinded by the volts.

AMPS = WATTS/ VOLTS

Example:

So if you were using a 20 amp breaker, 50 watt light bulb and 120 volt line, you would use the following. Remember, you want to use only 80% of the breaker capacity just to be safe and save worries later down the line.

Amps per light = 50 watt bulb / 120 volt

Each light would use .416 Amps.

80% of the 20 amp breaker would be 16 amps. Divide the 16 amp breaker by
.416 amps per light.

20 amps / .4545 amps per light = 38 lights.

Theoretically, you could use 38 lights.
trips is offline  
 
Reply With Quote
Old 11-20-2008, 06:14 PM  
fluxcapacitor
Junior Member
registry_dropdown_11151_25401
 
Join Date: Nov 2008
Posts: 9
Default

you are not allowed to use a 20A breaker for a lighting circuit in a dwelling unit (residential occupancy). It is against code (CEC). You must use a 15A breaker. It is common practise to not install more than twelve lights on a 15A breaker, regardless of the wattage of bulbs you use.
fluxcapacitor is offline  
 
Reply With Quote
Old 11-21-2008, 04:46 AM  
speedy petey
Lic.Electrical Contractor
registry_dropdown_722_25412
 
Join Date: Mar 2006
Posts: 453
Liked 41 Times on 28 Posts
Likes Given: 17

Default

Quote:
Originally Posted by fluxcapacitor View Post
you are not allowed to use a 20A breaker for a lighting circuit in a dwelling unit (residential occupancy). It is against code (CEC). You must use a 15A breaker. It is common practise to not install more than twelve lights on a 15A breaker, regardless of the wattage of bulbs you use.
Keep in mind that "CEC" stands for the Canadian electric code. We do NOT have either of these restrictions here in the US.
Considering the OP is in the US I think this is important to mention.
speedy petey is offline  
 
Reply With Quote
Old 11-21-2008, 09:38 PM  
triple D
Senior Member
registry_dropdown_5501_25440
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default yes 20 amp

Here in the states we can run a 15 or 20 amp lighting circuit. But not larger than that. And are only held to the max rating of all lights combined for circuit sizing, not number of them. Good luck on all your projects fellas....
__________________
[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]
triple D is offline  
 
Reply With Quote
Old 10-15-2010, 05:27 AM  
fasteddie
Junior Member
registry_dropdown_20291_49766
 
Join Date: Oct 2010
Location: Twin Lakes, WI
Posts: 2
Default

Aren't normal canned lights wired with #14 wire? Can these be used in a 20 amp circuit?


fasteddie is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
lower heat loss recessed lights. coach606 Electrical and Wiring 9 11-28-2012 02:42 PM
"electrical storm" in my breaker box-- buddyreid Electrical and Wiring 3 03-29-2008 09:16 PM
flickering lights in one room shan2themax Electrical and Wiring 1 07-08-2007 09:53 PM
Circuit breaker pops Vreelandjr Electrical and Wiring 10 11-09-2006 07:20 AM
Adding additional breaker for pool pump Jumper Electrical and Wiring 2 04-18-2006 08:11 PM

Newest Threads

LATEST SPONSOR DEALS