I have a circuit that has 3 outlets that work fine. Then there is a GFI Outlet which also works fine. There are four outlets and two small wall sconce lights that do not work. Using a plug tester (the little thing that plugs into a socket that has three lights) the 4 outlets say they are connected normal. As soon as there is a load applied, the indicators change to say that the HOT and GROUND are reversed. Nothing works when plugged in to these outlets. Additionally, if either (or both) wall sconce light(s) are turned on, the outlet changes from normal to HOT & GROUND REVERSED.

It worked fine the other day. I was out all day the next day and there was an electrical storm while I was gone. That evening the above situation existed.

I can't figure it out. Any ideas?



__________________
jersey-joe is offline  
 
Reply With Quote Quick reply to this message
Old 05-29-2008, 04:20 PM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Welcome Jersey-Joe:
I'm betting the common wire was used on a switch. A switch is supposed to only break the HOT wire; use the white wire only in the case of a switch leg and then it is supposed to be painted or tapped black indicating a HOT wire.
I would check the switch first and go from there.
Glenn



__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 05-30-2008, 07:08 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 992
Liked 109 Times on 89 Posts
Likes Given: 4

Default

Hot ground reversed is the indication of an open neutral. The white wire at one of the devices is loose. If you know the order they are wired the problem is in the last working device or the first not working device.
A very common cause of this problem is the use of the push in back stab connections. Put the wires under the screws if they are currently in little holes in the back.

__________________
JoeD is online now  
 
Reply With Quote Quick reply to this message
Old 05-31-2008, 11:39 AM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default Try this

Replace your gfi. Pay very close attn. to the way the wires hook up, and turn off power before even removing plug!!! That should fix er.

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Old 06-01-2008, 11:33 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

JoeD is right on this one. This is NOT a switched neutral, if it were it would work fine when the switch was turned on. This is an open (or compromised) neutral somewhere. The load is exposing it.

__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 06-02-2008, 07:53 AM  
jersey-joe
Junior Member
 
Join Date: May 2008
Posts: 4
Default

thanks all. i am going back to the RV today. I will check the existing outlets first for a compromised neutral. I have a new GFCI outlet that I bought to replace the existing one if the neutrals checkout OK.

__________________
jersey-joe is offline  
 
Reply With Quote Quick reply to this message
Old 06-03-2008, 01:21 AM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default Hey Joe

Please let us know what you find. Thanks....

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Old 06-03-2008, 05:56 PM  
jersey-joe
Junior Member
 
Join Date: May 2008
Posts: 4
Default

thanks to all who provided input.

I replaced the GFCI outlet and the same condition persisted. I pulled the outlets and switch out one by one and checked the connections. Found a loose neutral on, of course, the last outlet of the string.

__________________
jersey-joe is offline  
 
Reply With Quote Quick reply to this message
Old 06-04-2008, 01:06 AM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default Right on....

Did you mean the last outlet? like the one with only one wire? Or the first one with two wires? I only ask cause your situation would have only existed on that last plug if it was the end of the line. Anyway, good work Joe.....

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]


Last edited by triple D; 06-11-2008 at 12:05 AM.
triple D is offline  
 
Reply With Quote Quick reply to this message
Old 06-04-2008, 11:45 AM  
jersey-joe
Junior Member
 
Join Date: May 2008
Posts: 4
Default

the load side of the GFCI outlet went to a junction box. From the junction box one wire went to 1 outlet and another wire went to 3 outlets and the 2 wall sconces. The loose neutral was the first of the 3 outlets in a string. Just so happened it was the LAST outlet I checked.



__________________
jersey-joe is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Another pilot lite issue on my hot water tank dp2209 Plumbing Forum 2 12-31-2008 10:51 PM
Thermostat issue on baseboard heater papason HVAC 7 12-10-2007 11:00 AM
Entry door issue - Whoops! Mike P. Flooring 2 10-11-2007 10:05 PM
ANNOYING electirc cable issue! evansvillehousewife Electrical and Wiring 2 01-22-2007 06:39 PM
Wood flooring issue Rich9995 Flooring 0 06-28-2006 08:49 PM

Newest Threads

LATEST SPONSOR DEALS