DIY Home Improvement, Remodeling & Repair Forum > Appliances > HVAC > Cold Air Return Ducts




Reply
 
Thread Tools Search this Thread Display Modes
Old 08-20-2008, 07:16 AM  
chipper
Junior Member
Join Date: Aug 2008
Posts: 3
Default Cold Air Return Ducts

Is there a rule of thumb or formula to determine the amount of cold air returns required and where they should be placed?


chipper is offline  
 
Reply With Quote
Old 08-20-2008, 07:47 AM  
Hube
Senior Member
Join Date: Apr 2006
Posts: 114
Default

A forced warm air duct heating/cooling system should have a Return "area" that is at the LEAST equal to the Supply area.
In other words, if the Main Supply duct is 8x20 (160 sq in ) then the Return size should be at least 160 sq in or even approx 10 % more.
Hopefully, the Supply caculation and the Unit (btu and cooling tonnage) are sized properly in the first place via Manual J and Manual D to determine the correct heat loss/gain.

As for placement of Returns,they are best on the floor opposite and farthest away from the Supplys which are best when placed on the exterior of the rooms (under windows)
Ex; Supplys on the exterior of the room
Returns on the interior of the room
note; for cooling purposes only, Returns can be placed in the interior high-wall location, or for both heating and cooling they can be located in the SAME stud space and activated by installing a damper in the lower grille.



Last edited by Hube; 08-20-2008 at 08:02 AM.
Hube is offline  
 
Reply With Quote
Old 08-22-2008, 07:41 AM  
chipper
Junior Member
Join Date: Aug 2008
Posts: 3
Default

Thanks for the info. We just moved into a house that was built in 1869 and I'm trying determine if the duct work is correct. There is no duct work to the 2nd floor which I'm in the process of adding. I have limited space on the 2nd floor so I have added a 6" duct to the master bedroom, 5" to the 2nd largest bedroom, 4" to the smallest bedroom and 5" to the bathroom. I only have enough room for a 6" return duct. Is that enough?
The den on first floor has 2 heating ducts and 2 return ducts. I'm assuming I should remove one of the return ducts?
The kitchen has 2 heating ducts and 12' by 12' sunroom attached. Should I move one of the heating ducts to the sunroom and add a cold air return?
I'm also going to replace the 40 year old furnace with a Trane XV95.
chipper is offline  
 
Reply With Quote
Old 08-22-2008, 10:07 AM  
Hube
Senior Member
Join Date: Apr 2006
Posts: 114
Default

In order to get the proper sizes for a heating/cooling unit and a supply and return ductwork one would have to have completed a Manual J and a Manual D calculation sheets. These calculations will take into account the amount of windows,size of rooms, insulation r value, orientation and the climatic temperatures of the area you live in. Doing it any other way would be a foolish guess.
A lot of math goes into figuring how much supply and return is needed.
eg; a 4" diam = approx 12 sq inches.
a 5" diam = approx 20 sq inches
a 6" diam = approx 28" sq inches

That's a total 60 sq inches of area for those 3 ducts you are figuring on using in the upper floor. But since return air should be at least equal to the supply that means the 6" return you are figuring to install will fall far short of doing any real good,if any.
If you are putting supply air in that adds up to 60 sq inches then you should have at LEAST that amount in return fromthat area.

Note; DO NOT install any return in a bathroom or kitchen area.(odor)
In all, you would be wise to have a heat loss/gain and duct sizing done, then you will know for sure that any furnace(btu,s) and duct sizing will be best for you .
if you have more questions feel free to ask.
Hube
Hube is offline  
 
Reply With Quote
Old 08-25-2008, 06:36 AM  
chipper
Junior Member
Join Date: Aug 2008
Posts: 3
Default

Thanks for the info. The new furnace will be installed in 2 weeks so I will continue with my ductwork and then ask the installer to make some recommendations.
chipper is offline  
 
Reply With Quote
Old 03-04-2011, 07:17 AM  
elle55
Junior Member
Join Date: Mar 2011
Location: Ottawa, Ontario
Posts: 1
Default

HI I just joined and have a question. I plan to add a bathroom where the existing cold air return is, and wanted to know how to move it.
elle55 is offline  
 
Reply With Quote
Old 11-26-2012, 12:55 PM  
papa56
Junior Member
Join Date: Nov 2012
Posts: 1
Default

hello I have an old cold air return system sheetmetal on floor joist. There are these big 8x32 inch grates, wonderind if I could replace them with smaller grates. Thanks John
papa56 is offline  
 
Reply With Quote
Old 11-26-2012, 01:54 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

For exhaust fans, the intake area in the volume to be ventilated should be 4X the fan blade swept area.
Wuzzat? is offline  
 
Reply With Quote
Old 07-14-2015, 01:50 PM  
TNprogrammer
Junior Member
Join Date: Sep 2009
Posts: 4
Default

I know this thread is a bit old, but I've been doing some research on this topic as we just finished out a walk-in attic space and added two air vents in the ceiling. We did not originally add a return in the room, but I see now that we are going to have to add one. the room is 15x12.5. Too much warm stale air is getting caught up in the room and on hot days the coolest we can get it is 79-80 degrees. Also, it has a high ceiling of 9.5 feet.
Looking at what a lot of guys mention about return volume needing to be equal to forced air volume, I look at how our new house was originally set up and there is no way our system was set up to return as much air volume as it puts out. We have one centrally located return (20x30) in the upstairs hallway ceiling and 8 forced air vents throughout the various rooms.
I wonder if the idea of having only a single centrally located return came about as houses began being built with more open floor plans, allowing less obstructions back to the return.
TNprogrammer is offline  
 
Reply With Quote
Old 07-14-2015, 01:57 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,845
Liked 1402 Times on 1236 Posts
Likes Given: 2423

Default

The size of the screen may be misleading, the actual duct size may be smaller.


nealtw is offline  
slownsteady Likes This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Cold Air Return Question Richwho HVAC 12 01-14-2009 08:55 AM
do we need cold air return registers in every room sumat HVAC 3 01-12-2009 05:54 AM
Enclosing a room that has a central air return vistav HVAC 5 01-29-2008 02:21 PM
Questions about return alkemyst HVAC 3 11-03-2007 09:27 AM
Moving a cold air return? WestBentley HVAC 7 03-02-2007 11:36 AM