Old 02-28-2009, 04:13 PM  
mrc59
Junior Member
 
Join Date: Feb 2009
Posts: 10
Default Outdoor GFI tripping, wires have voltage

I wired a detached greenhouse with one 120V and one 240V circuit, and all wires run though the same conduit. The conduit has one outlet mounted on the side of the house, with a GFI. The outlets inside the GH are protected by the house GFI. The outlets are for lights and a fan. The 240V line is for a heater. Wire size, box load, load/line lugs downstream from the GFI are all proper.

Recently, the GFI started tripping when reset. I disconnected the downstream lugs, and the GFI works properly. When I tried to test resistance with a digital (Fluke) multimeter, I find low AC voltage, around 2VAC between hot and ground, and hot and neutral. With the 240V breaker tripped, there is less voltage, perhaps 0.6VAC.

That weirded me out! I traced the voltage leak all the way back to the breaker. With one lead on the neutral bus, one lead on the breaker script, breaker tripped, I find between 0.6 and 2.3 VAC!

I know GFI's measure the difference in current, but I can't even begin to check resistance in the downstream circuit with the low voltage leak.

Is this a peril of a digital meter?

I can't remove the GFI, but I need power back for the fan!

Anyone have an idea where to begin?



__________________
mrc59 is offline  
 
Reply With Quote Quick reply to this message
Old 02-28-2009, 04:44 PM  
Blue Jay
Senior Member
 
Blue Jay's Avatar
 
Join Date: Jun 2008
Location: La Rue, Ohio
Posts: 252
Liked 10 Times on 10 Posts
Likes Given: 18

Default

Sounds like the voltage is induced, you would need to disconnect all wires at the breaker box that are running close to these wires to get rid of it. (including the neutral and ground)



__________________
Blue Jay is offline  
 
Reply With Quote Quick reply to this message
Old 02-28-2009, 10:32 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Is the 120V GFI that keeps tripping, in the main panel or did you run this from an existing circuit from the house?

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 03-01-2009, 06:03 AM  
mrc59
Junior Member
 
Join Date: Feb 2009
Posts: 10
Default

I figured the voltage was induced all right, and never noticed it before. The breaker box is full of dual breakers. Lots of circuits! This is a sub panel.

This is a dedicated circuit to the GH. From the panel to the GFI (outdoor) receptacle, then on to the GH interior.

I'm starting to suspect the GFI itself. It looks like there is a mess of spider/bug crud within. I don't have spare handy, but it's been out there for several years.

__________________
mrc59 is offline  
 
Reply With Quote Quick reply to this message
Old 03-01-2009, 07:29 PM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default check this....

make sure that all the ground wires in the sub panel are on a dedicated ground bar. And that it is mounted to the breaker box directly. Then check to see that all the neutral wires are on the same neutral bar, and that bar is in no way connected to the grounds or the panel box. Then make sure this practice is carried through all of the wiring related to green house. If your gfi will hold, with the outgoing wires disconnected, work your way through the circuit, hooking up each thing in line till you find the one that upsets the gfi. And digital meters suck in these cases, (in my experience) Good luck....

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Old 03-02-2009, 03:59 AM  
mrc59
Junior Member
 
Join Date: Feb 2009
Posts: 10
Default Thanks and thought so

Thanks! Will do. I still have the "vintage" Sears analogue multimeter



__________________
mrc59 is offline  
 
Reply With Quote Quick reply to this message
Reply


Tags
gfi, outdoor, tripping, voltage leak

Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Intermittent Problem with Decorative Low Voltage Fixture mman Electrical and Wiring 2 11-07-2008 07:00 AM
Whole-House Voltage Regulator vs. Surge Suppressor SeekingInfo Electrical and Wiring 2 09-26-2008 11:04 PM
GFI Tripping and troubleshooting jwar Electrical and Wiring 4 02-08-2008 10:14 AM
HELP! Need to find cable locator for low voltage Johnboy555 Electrical and Wiring 6 01-02-2008 11:02 AM
loose/left-over wires in remodel skopper Electrical and Wiring 5 07-20-2006 05:58 PM

Newest Threads

LATEST SPONSOR DEALS