Default GFCI Outlets Outdoors/Garage

I was plugging in my bug zapper for the season and it occurred to me that the outdoor outlet was not GFCI. I'm assuming it should be and would like to replace it, but I wanted to make sure that's the right thing to do and if it's as simple as just buying a GFCI outlet.

Additionally, when the house was inspected (by a lazy old guy named "Junior" ), he said he assumed there was a GFCI outlet in the garage even though the former owner had put a 6 outlet adapter over it. I got curious this weekend and took the adapter off, and there is none. Should there be there, too? It's dead center-vert and horz--of the wall that has the water heater on it.

There are GFCIs in both bathrooms and one in the kitchen for the outlet on one side of the sink, but not the other. What is the rule here? If someone could tell me every place that should have a GFCI, I'm happy to go around and correct it.

Karleen



__________________
SavvyCat is offline  
 
Reply With Quote Quick reply to this message
Old 03-16-2009, 12:58 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

The "rule" is whatever it was when the house was built.

You can do whatever you want to upgrade to recent code requirements.

Here is a history. Click on the 2008 link for current requirements: GFCI Outlet Purpose and GFCI Location History



__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 03-16-2009, 02:19 PM  
SavvyCat
Member
 
SavvyCat's Avatar
 
Join Date: Jan 2009
Location: DFW Area
Posts: 77
Liked 1 Times on 1 Posts
Likes Given: 4

Default Thanks!

That was a very interesting site. If I understood what I was reading, since the house was built in 1982 neither the garage nor outdoor outlets were to code unless someone "uncoded" them later. I suppose nothing could be harmed by making a few changes.

Thanks!

__________________
SavvyCat is offline  
 
Reply With Quote Quick reply to this message
Old 03-16-2009, 03:27 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Quote:
Originally Posted by SavvyCat View Post
I suppose nothing could be harmed by making a few changes.
You have only safety to gain by adding GFI protection.
__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 03-16-2009, 07:55 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,216
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Before you go to the trouble of installing new outlets, check to see if these outlets are already GFI protected. Trip all the GFI's in the home and then test these outlets for power. It might be that these are regular oulets being GFI protected from one (or more) of the existing GFI's in the home. If you find you have no power then, reset the GFI's one by one and this will tell you where your protection is coming from. If you have power at the outlets in question with all GFI's tripped then, the outlets are not GFI protected and GFI's would be in order.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 03-17-2009, 11:33 PM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default f.y.i.

you can also go to any hardware store that sells electrical stuff and get a plug tester that has a gfi test button on it for around five bucks. You can plug it in anywhere and push the test button, if power stays on, it is not on a g.f.i. If you use these on an arc fault protected circuit, they will trip the breaker. Good luck....

__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Old 03-18-2009, 10:23 AM  
SavvyCat
Member
 
SavvyCat's Avatar
 
Join Date: Jan 2009
Location: DFW Area
Posts: 77
Liked 1 Times on 1 Posts
Likes Given: 4

Default

Good advice from both. I'll add it to the list (my list is getting kinda lengthy).

__________________
SavvyCat is offline  
 
Reply With Quote Quick reply to this message
Old 05-04-2009, 12:30 AM  
electrical contractor
Junior Member
 
Join Date: May 2009
Posts: 9
Default

A GFI tester shouldn't trip an arc fault breaker. Arc faults are sensative to power spikes and arcing voltage where a GFI measures the difference between the power going out and coming back to make sure there is no leakage to ground. The tester is the best option. Most houses from 82' had either a GFI breaker or a GFI in the garage that controlled both the garage and outdoor receptacles. If you test to find the first outlet in the sting and install a GFI there, your one GFI will protect all the outlets after it.

__________________
electrical contractor is offline  
 
Reply With Quote Quick reply to this message
Old 05-04-2009, 01:25 AM  
electrical contractor
Junior Member
 
Join Date: May 2009
Posts: 9
Default

you can find more info about this at Ground Fault Circuit Interrupter(s) GFCI (NEC Code - Tripping GFI - Installation)

__________________
electrical contractor is offline  
 
Reply With Quote Quick reply to this message
Old 05-04-2009, 10:29 PM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default welcome new guy or girl...

If you are on a arc fault protected circuit and you have any load running on that circuit (any) and you touch the ground and neutral together, it will trip the a.f.c.i. breaker. It just so happens that this is how a g.f.i. plug tester works. Try one out sometime, youll be re-setting the arc fault.



__________________

[COLOR="DarkGreen"][FONT="Franklin Gothic Medium"]See my work-Check out my album. "Git 'Er Done":D [/FONT][/COLOR]

triple D is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
GFCI Circuit 3dognight Electrical and Wiring 7 06-14-2009 09:00 AM
GFCI problem Remodeler Electrical and Wiring 21 05-04-2009 01:22 AM
Need advice on a material to use for outdoors that is breathable yet private. DebbieG Decorating and Design 1 10-26-2008 04:31 PM
Installing Slate tiles outdoors VictorC General Home Improvement Discussion 0 10-30-2006 07:30 AM

Newest Threads

LATEST SPONSOR DEALS