Default Is 20 Amp breaker too big for a fluorescent light

Background:

Built a basement closet which contains my (2) FPE 200 amp service boxes. I just mounted a T8 Two strip fluorescent light on the ceiling controlled by a single pole switch. All wires are ran...

Question:

I have a leftover 20 Amp breaker available (American Single pole HARC type), is this too big for this single light circuit? I have numerous open slots for new circuits.

If so, I don't want to buy a 15 Amp breaker due to big $$'s, so should I just tap into an existing 15 Amp circuit?

Thanks for your responses,

Todd


toadylama is offline  
 
Reply With Quote
Old 07-07-2009, 08:03 PM  
speedy petey
Lic.Electrical Contractor
registry_dropdown_722_32073
 
Join Date: Mar 2006
Posts: 453
Liked 41 Times on 28 Posts
Likes Given: 17

Default

Quote:
Originally Posted by toadylama View Post
I have a leftover 20 Amp breaker available (American Single pole HARC type), is this too big for this single light circuit?
No. The breaker protects the circuit wire, not the fixture.

Quote:
Originally Posted by toadylama View Post
......, so should I just tap into an existing 15 Amp circuit?
I would. I see NO reason whatsoever for running a new 20A circuit to install one fluorescent light.


speedy petey is offline  
 
Reply With Quote
Old 07-08-2009, 12:43 PM  
toadylama
Junior Member
registry_dropdown_15471_32099
 
Join Date: Jul 2009
Posts: 3
Default

Thanks for the reply.

My real concern is using a 20 Amp breaker for a light only circuit (which is usually 15 AMP) and posing a greater possible fire hazard.

So, if I opted for the 20 AMP breaker (easier), does anyone foresee any issues?

thanks, todd
toadylama is offline  
 
Reply With Quote
Old 07-08-2009, 06:08 PM  
JoeD
Contractor
registry_dropdown_728_32109
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 1,076
Liked 130 Times on 106 Posts
Likes Given: 4

Default

If the circuit is wired with #12 wire then you can use the 20 amp breaker. If it is wired with #14 then you must use a 15 amp breaker.
JoeD is offline  
 
Reply With Quote
Old 07-08-2009, 08:16 PM  
speedy petey
Lic.Electrical Contractor
registry_dropdown_722_32120
 
Join Date: Mar 2006
Posts: 453
Liked 41 Times on 28 Posts
Likes Given: 17

Default

Quote:
Originally Posted by toadylama View Post

My real concern is using a 20 Amp breaker for a light only circuit (which is usually 15 AMP) and posing a greater possible fire hazard.
This is not a concern at all. The breaker protects the circuit conductors, not the light fixture.
speedy petey is offline  
 
Reply With Quote
Old 07-11-2009, 07:41 PM  
toadylama
Junior Member
registry_dropdown_15471_32194
 
Join Date: Jul 2009
Posts: 3
Default

Wired it up last night...works great with 12-2 wire and the 20 amp breaker!

Thanks for the tips.
toadylama is offline  
 
Reply With Quote
Old 07-11-2009, 08:05 PM  
bkplasma
Junior Member
registry_dropdown_15537_32195
 
Join Date: Jul 2009
Posts: 10
Default

Glad it works for you. Now you have plenty of room to add several other lights on same circuit in future.


bkplasma is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
fluorescent ballast- bad smell JoJoBeans Electrical and Wiring 3 02-20-2009 07:39 PM
rewire light from switch to light davidh424 Electrical and Wiring 3 01-12-2009 08:56 PM
Updating look of recessed fluorescent fixtures? TaskBoy Electrical and Wiring 3 06-06-2008 02:06 AM
ceiling light wiring affecting light in another room johnm Electrical and Wiring 4 05-25-2008 12:55 AM
moving breaker box shan2themax Electrical and Wiring 4 02-12-2008 07:41 PM