replace vapor barrier?

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

gopher

Member
Joined
Sep 18, 2009
Messages
8
Reaction score
0
hey guys
i am doing some remodeling in my house
I didn't like the wood paneling so I ripped it out
of course it was glued to the dry wall so the drywall had to be replaced
i ripped out the drywall to discover some wet insulation
i ripped out the insulation to discover the vapor barrier was wet
i ripped out the vapor barrier to discover some holes in the brick mortar
i filled in the mortar holes with hydralic cement
now i need to replaced the mositure barrier, it was a thick cardboard like material with silver foil on the outside
problem is the vapor barrier goes inbetween the wall ties and the studs...
so what do i do to replace the vapor barrier?
1. rip out the brick veneer and do from the outside?
2. rip out the wall ties and do from the inside?
3. ??? any other ideas?
i really dont want to rip apart the brick wall im open to any ideas
 
An alternative to installing vapour barrier is to go with an insulation that doesn't need one, on either side.

That insulation is extruded polystyrene foam, like the blue "Roofmate" insulation. It's a lot more expensive, but it also offers a stabilized R value of R5 per inch thickness compared to about 3.5 for fiberglass.

Basically, you just cut the extruded polystyrene into slabs to fit between the stud spaces and use expanding polyurethane foam to caulk around their perimeter, thereby gluing them in place as the foam cures. Once cured, just cut off the excess foam, and you're good to start drywalling.

There are two kinds of polystyrene foam insulation; expanded and extruded. Expanded is the white stuff that seems to be made of tiny "beads". Extruded is the blue or pink stuff like Roofmate. They use much more blowing gas when making expanded polystyrene, and that generally results in the beads being interconnected. If those beads are interconnected, than the foam is permeable to air and water, and can even become water logged as the foam beads inside it fill up with water. Extruded polystyrene foam insulatin is made with much less blowing gas, so the gas bubbles inside it don't interconnect, and so it's effectively impermeable to air. If air can't get into the stuff, you don't need a vapour barrier to keep air out of the stuff.

But, all blown foam insulations will have a much higher R value when they're first manufactured. As the blowing gas inside the insulation escapes and is replaced by air, the R value drops substantially. So, don't listen to any one offering to sell you R13 foam insulation. They're quoting the initial R value (or just plain lying), not the stabilized R value, which for polystyrene of both kinds, will be close to R5 per inch.
 
i filled in the mortar holes with hydralic cement

Please don't do that again.

It's important when repointing bricks to ensure that the mortar holding the bricks together is softer and weaker than the bricks. That's because if the both get equally wet in a rain, and then the night time temperatures drop below freezing, you want the mortar to crack and break to relieve any stress in the brickwork rather than the bricks.

That's cuz you can always repair and replace the mortar. Fixing damaged bricks ain't so easy. So, next time use a normal brick mortar than a hydraulic cement.

PS: Add some hydrated lime to your brick mortar to help it hold on to moisture and stay workable longer. Some brick mortars just about turn into sand when you're working with them. Adding hydrated lime helps retain moisture in the brick mortar and greatly extends it's working time. It doesn't loose moisture by capillary pressure to the surrounding bricks nearly as rapidly, and that allows you to work with it longer. Wetting down the surface of the bricks in advance also helps, but it's really best to do both: Wet down the surface of the bricks and wait for that surface to dry before apply mortar to it, but use some hydrated lime in your mortar to keep the mortar plastic and workable for a much longer time.
 
ok i understand about the brick mortar, it was only 2 holes so i can remove the hydralic cement and refill with actual brick mortar.

But i have a question on the foam. its sounds like it will only fill in between the studs. wont the outside of the studs still be exposed??
 
also do i cut the foam to fit tightly in between the beams and foam on the face of it? or do i cut it slightly smaller and leave a gap and fill in the gap with the foam?
 
anyone car to comment on my questions??? please!
 
Your vapor barrier should have been on the warm side (room side) of the insulation for your climate.

After you tear out the insulation, you should at least find sheathing or something similar. The layer behind the brick should be a moisture barrier that can breathe.

What year was the house built in? There were some strange things going on Detroit, just as they are now.

It is a good thing you got rid of the fiberglass, which is a poor excuse for insulation and loses a lot of insulating value with as little as 1/2% to 1 1/2% moisture. Once it is wet, it will not dry out.
 
moisture barrier is want i meant when posting the original title.
i have removed the original moisture barrier from the inside due to water damage and insects. Now i need to replace it from the inside which is technically impossible since there are wall ties holding up the brick veneer. So i need to know how to rig this up from the inside so that it will last.
 
Gopher:

Sorry for not responding earlier. I'm preparing a case for the Manitoba Court of Appeal, and it's taking all my time. I'm not a lawyer, and that's presumably what makes it harder.

To answer your questions:

If you only used hydraulic cement in two spots, I wouldn't bother replacing it. It's not like the entire lattice mortar is stronger than the bricks. Maybe next time you're doing any brickwork and you have the tools out anyhow, see if you can pull out the old hydraulic cement and replace it with mortar. You probably won't be able to cuz hydraulic cement expands as it cures, and I expect it's wedged into that brickwork real tight by now. If you can't get it out, forget about it. If you can, replace it.

You could always drill through the hydraulic cement with a masonary bit and hammer drill, and then chip the hydraulic cement to pieces with a small chisel.

But i have a question on the foam. its sounds like it will only fill in between the studs. wont the outside of the studs still be exposed??

Sure, but leaving the wall studs exposed on their outside will only result in a bit of heat loss. Remember that the R value of wood is approximately 1 per inch. So a wall stud offers an R value of about 3.5 compared to a 3.5 inch thick slab of extruded foam insulation that will give you about 17. So, eventually, if you smoke or burn candles in your house, you might expect to see dark lines forming over the wall studs due to something called "Brownian Motion" which is where tiny dirt particles (approaching the size of individual molecules) cling to the coldest parts of the wall because of the loss of energy when they contact those cold surfaces. At those relativistic sizes, then thermal energy becomes kinetic energy and back again easily, so when tiny particles hit a cold wall, they can loose ALL of their kinetic energy to the wall and remain on the wall. Since that happens mostly over the coldest parts of the wall, the dirt collects over the studs, but not between the studs. And, if you give it some time, you can even see exactly where the drywall screws holding the drywall to the studs are located. And, it's all thanks to Brownian Motion and the Twilight zone between Newtonian physics and Quantum physics.

But, rest assured that a Magic Eraser and some elbow grease will eliminate those Brownian particles. You do, however, need to use a Magic Eraser because the size of the particles we're talking about are tiny enough to fit in between the microscopic roughness on even high gloss paints, and so cleaning with a sponge, brush or rag ain't good enough. You gotta use a Magic Eraser which has fibers small enough to clean between the microscopically small bumps on high gloss paints.

Not sure if I addressed the point of your question. On no other building will you find any insulation on the exterior of the wall studs, unless the siding of the building acts as an insulation.

PS: so you know: The ENTIRE PURPOSE behind a moisture barrier or vapour barrier is to prevent warm moist air from getting into the fiberglass insulation. The reason why you want to avoid that is because condensation inside fiberglass insulation reduces it's R value AND insulation works by keeping air stagnant, and therefore wet insulation takes forever to dry out. So, wet insulation in contact with wood studs provides the conditions necessary for the wood rot fungus to start growing on the wet wood. That can lead to wood rot growing on your wall studs behind the wall where you can't do anything about it, and that's often what people talk about when they say a house has "mold".

By using extruded polystyrene foam insulation, warm humid air can't get inside it in the first place, and so it doesn't need a vapour barrier to prevent warm humid air from getting inside it and causing all the problems that occur with fiberglass insulation when that happens. If warm moist air penetrates through a gap between the foam insulation and the wood stud, it might form condensation, but that condensation will dry out come spring or summer, and won't cause any harm. Remember, it's the nature of fiberglass insulation in keeping air stagnant that prevents that condensation from drying out. Condensation outside of fiberglass insulation dries out fine.

Re: the outside of the studs: It's true that the outsides of the studs will be exposed to temperature and humidity changes that occur outdoors, but the bare wall studs in every unfinished garage in North America are exposed to the same environmental changes. Your wall studs will last just as long as the studs in any unfinished garage in Detroit, which, provided the roof don't leak or the garage burn down, will be as long as the wall studs in any structure, finished or not.


also do i cut the foam to fit tightly in between the beams and foam on the face of it? or do i cut it slightly smaller and leave a gap and fill in the gap with the foam?

By "beams" do you mean wall studs?

I don't think it matters much. If it were me, I'd cut as close as I can without cutting the slab too large, and then secure it in place with door hanging shims wedged between the foam slab and the studs and then caulked around the perimeter of the slab with expanding foam. Once that foam cured, I'd pull the shims and cut the expanding foam off flush with the front of the studs. I might fill in where the shims were too, just to be obsessive/compulsive/neurotic, er, I mean a perfectionist.

Now i need to replace it from the inside which is technically impossible since there are wall ties holding up the brick veneer.

That part I don't understand. I can't imagine a wooden stud wall supporting the weight of a brick wall. I expect what you're referring to as "wall ties" were simply metal strips fastened to the studs so that the brick layers could set the brick wall a uniform distance from the wall studs. If that's the case, those ties don't hold up anything. There has to be a steel lintel under that brick wall to support it. STEEL or a short thick slab of solid stone or reinforced concrete are the ONLY things strong enough to support the weight of a brick or concrete block wall. Don't even daydream that a wood stud wall could ever support the weight of a brick wall.

Those things between the brick wall and the wood stud wall are there for some other purpose than supporting the brick wall.
 
Last edited:
ok understood

i was concerned about not having a moisture barrier on the outside of the studs, but it sounds to be a non-issue. I was more concerned about the moisture barrier protecting the studs from rotting from possible water damage, but now that I understand the actual function of the moisture barrier, the foam sounds like the perfect fix.

i know the wall ties don't hold up the wall but they do prevent it from getting pushed over, thats why i didnt want to remove them.

Nestor thanks for all the information It is appreciated. I will soon be getting back to work!
gopher
 
The moisture barrier is required by code to be outside the studs under brick veneer with a 1-4-1/2" max. gap to the sheathing OR the mortar or grout fill over a weather-resistant membrane... IRC 703.7.4.2

Water resistant membrane not required if sheathing is water repellent... 703.7.4.2
This would be the foil covered foam sheathing you removed. Now you have nothing to prevent moisture from getting to the edges of your studs, and nothing to hold the wall in rack from the shear forces. (Wind, earthquake, etc.)
The ties are required on brick veneer every 24" max. horizontal spacing..... IRC 703.7.4.1

I would try to install builder's paper (in strips, overlapping by 2") on the studs and install
the foam board in the bays -if needed there is a 6.5R factor for 2x4 walls: Dow at Lowe's: 1" x 8' x 4' R-6.5 Polyisocyanurate Rigid Foam Insulation

And a Simpson strap inside to prevent racking: WB/WBC/TWB/RCWB Wall Bracing
Be safe, Gary
 
i did not remove the wall ties so i dont think it safe structurally
how do you suggest fastening the paper to the outside of the studs?
 
What exactly is the purpose of having a moisture barrier outside of the studs?

Is it to prevent moisture from getting into the wooden stud wall system?

If so, they why couldn't he compensate for the potential rotting of the bottom plate on his wall by putting borate rods (Impel or Cobra rods) into his bottom plate to prevent wood rot of that bottom plate, and just let the outside surface of the wall studs get wet the occasional time that there's a hurricane in Detroit?

I know that's not what the code says, but wouldn't that protect the wall system from moisture? After all, if moisture is going to penetrate the brickwork, almost all of that moisture is going to dribble down the inside surface of the brick veneer. It's not going to jump from the brick veneer onto the insulation in anything less than a hurricane force wind, and in this case, if Gopher has extruded foam insulation between his studs, that water is gonna drip off the insulation and just get the wood studs wet for a day or two until they dry. In that case, the only concern is the bottom plate of the exterior wall which may get wet from water penetration through the brickwork.

PRG, Inc. - Impel Rods

Gopher:
Borate rods (either Impel or Cobra rods) are a borate compound that dissolves in water. Borate rods are preferred by owners of log homes because borates are highly soluble in water, and so borates are the ONLY wood preservative that will diffuse through the entire cross section of a log to protect it from wood rot. Telephone utilities use both Impel and Cobra rods to protect telephone poles from rotting in the ground, and it's because the borates migrate through the entire cross section of the pole. The wetter the wood, the faster the borates dissolve and diffuse. Unless the wood is wet, the borates don't dissolve and don't diffuse.

I have 6 borate rods in each of many of the wooden window frames of my apartment block. If those window frames ever get wet to the point where they might rot, the borate rods begin to dissolve and the borates diffuse throughout the wood killing mildew and mold, including the wood rot fungus.

Borate wood preservatives are much more popular in Europe. They're not common here in North America because we tend to go with either pressure treated lumber of copper and zinc naphthalene end cut preservatives here. The beauty of borates is that they they remain unaffected until the wood gets wet, and then they dissolve and disperse throughout the wood to protect it from wood rot (and other fungi). Also, borates are the only wood preservative that's environmentally friendly. They are highly toxic to fungi and molds, but mammals like people and pets can just about eat borates without getting sick. Your typical borax used for doing laundry contains borates similar to those used in Impel rods and Boracol wood preservatives, and we wash our clothes in that stuff and wear those clothes all day with no health effects whatsoever. Also, although everyone calls them "Impel" rods, the liquid equivalent goes by many different names, depending on who's selling it. It can be called Borocol, Boratreat, Bora-Care, etc. It's all the same stuff being sold under different names.

PRG, Inc. - Impel Rods

Borates, Impel Rods, Cobra Rods, for natural pest control and rot protection in Log, Timber and Wood homes

Impel Borate Rods - Log Preservatives

But, what to do depends entirely on WHY your local building code requires a moisture barrier between the brick veneer and the wood stud wall. Hopefully GBR would know if that's because of water penetration into the wall system or not. If it is, then water will drip down your wall studs, but you may need to do something to protect the bottom plate of your wall.

The borate rods (Impel rods) you might find online are huge, often 3/4 inch in diameter by 4 inches long. Those are meant for logs in log homes and telephone poles. In my window frames I have 6 millimeter diameter by 60 millimeter (1/4 inch diameter by 2 3/8 inch long) Impel rods in 5/16 inch diameter holes, and I'd suggest those would be more than adequate for the bottom plates on your exterior walls.

What I'd suggest is that you finish your wall normally, and then drill through the baseboard into the bottom plate and insert an Impel rod in each hole. The hole has to be slightly larger in diameter than the rod to allow for the swelling of the rod that occurs as the Borate rod absorbs moisture and gets to the point of dissolving in the moisture in the wood. The depth of the hole is irrelevant. But, once a borate rod starts to swell, you cannot remove it from the hole it's in. Not easily anyhow.

I'm thinking that protecting the wood in your wall from rotting may be the second best alternative to preventing it from getting wet in the first place.
 
Last edited:
Gopher:

Clearly, the thing you gotta do is find out exactly why your local building code requires a moisture barrier on the EXTERIOR of the wood studs. If it's simply to prevent water that drips through gaps in the mortar from getting onto the exterior of the wall, then I'd:

Open up gaps in the brick mortar right at the bottom of the wall and as high up on that wall as you can. A hole every 4 feet or so would be sufficient, and if possible it would be best to have the holes angled downward so that rain water drains outward rather than into your wall. The idea here is to mimic attic ventilation to dry the wall in winter; kinda like attic ventilation applied to walls. Air between the stud wall and the brickwork will be heated by heat loss from the house and will rise in the gap between the stud wall and brick veneer to escape through the holes near the top of the wall. That will draw cold dry outdoor air into that same space. And, as it warms from heat loss through the insulation, it too will warm and absorb any moisture present and carry it to the outside through the top holes as well. This heat loss driven convective current will continue 24/7 all winter long, keeping your wall dry. Putting the holes through the vertical brick mortar joints at a downward angle will allow air convection through the wall, but will prevent rain penetration through it.

The second thing I'd do is finish your wall normally with baseboards, etc. And, drill through the baseboards with a 1/4 inch drill and slide in some 6 millimeter diameter Borate rods. If the bottom plate of your wall ever gets wet enough that there is a risk of wood rot, the borate rods will dissolve and disperse throughout the wood, killing any mold or fungus that might feed on that wood. You can buy small plastic caps to fill those holes from any place that sells O-rings. That's because most places that sell O-rings also rebuild pneumatic and hydraulic valves, and once the valve is rebuilt, they put plastic caps in all the ports to prevent dirt from getting into the valve. You can use those same caps to plug the holes in your baseboards. You want to drill the hole deep enough so that the 60 mm (2 1/2 inch long) borate rod is centered in the bottom plate of the wall, preferably between studs so that your drill bit doesn't hit any nails.

But, the immediate order of business is to find out what's behind the requirement to have a moisture barrier on the exterior of that inner wood stud wall.
 
What exactly is the purpose of having a moisture barrier outside of the studs?

Is it to prevent moisture from getting into the wooden stud wall system?
********************************************************

Yes, a MOISTURE barrier is needed on the exterior side of the studs to protect the studs and also any insulation. A moisture barrier breathes.

A VAPOR barrier is needed towards the room side of any heated exterior walls(between the drywall and the studs) . A vapor barrier, usually a 6 mil poly sheeting will not breathe.

Now go back to whatever you were doing before getting involved in building practices that you seem to know not too much about.:(
 