Default precisley!

That is exactly correct Joe, your trouble shooting skills are right on. The neutral slowly burned itself the rest of the way apart over time. The breaker would of never held, from the time the screw was installed. Was this person a licensed electrician by chance?


__________________
See my work-Check out my album. "Git 'Er Done":D
triple D is offline  
 
Reply With Quote
Old 08-09-2010, 10:14 AM  
jsbeckton
Junior Member
Join Date: Aug 2010
Posts: 15
Default

Quote:
Originally Posted by triple D View Post
That is exactly correct Joe, your trouble shooting skills are right on. The neutral slowly burned itself the rest of the way apart over time. The breaker would of never held, from the time the screw was installed. Was this person a licensed electrician by chance?
He is not a licenced electrician. I still am having trouble understanding how a open neutral can cause it to be at 120V?

Also, should the breaker have tripped?


jsbeckton is offline  
 
Reply With Quote
Old 08-09-2010, 03:52 PM  
john4153
Junior Member
Join Date: Aug 2010
Location: Cleveland, Ohio
Posts: 13
Default

Let me try to explain why one can see full voltage or almost full voltage from the com to ground, when com is open. Refer to the following diagram. I have represented each load as a resistance.



It is important to note that the voltmeter draws almost no current. Consider first the switched load. If it is switched on, there is a direct path from hot to the com side. Since there is no current drawn by the voltmeter, there is no voltage drop across that load resistance. Thus, one sees the full voltage when measuring to ground. Now assume the switched load is off. Why can one still see a voltage in most cases? Well there is always some leakage which may be a very high resistance and might be measured. But more commonly in modern equipment, there is going to be some real, but very small load, such as an LED (whether seen or not), maybe a defrost timer, etc. In that case, the no-current voltmeter will see the voltage. That is why I suggested applying a load across the points being measured.

Now, are there instances in which an open com may result in no voltage reading from com to ground? I am sure there are, but considering the complexity of the wiring in our houses and the number of potential non-switched loads on the com lines down-stream of the break, it might be uncommon. Also, given the close proximity of the com wire to the hot wire, coupling to the field around the hot line to com (think of a radio antenna) could give a voltage reading. Just look at how the value on an AC voltmeter will tend not to be zero when one lead is grounded and you touch the other or just leave it in free air.

Regards, John
Click image for larger version

Name:	OPEN COM.png
Views:	1658
Size:	14.1 KB
ID:	2129  
john4153 is offline  
 
Reply With Quote
Old 08-10-2010, 11:30 AM  
jsbeckton
Junior Member
Join Date: Aug 2010
Posts: 15
Default

Quote:
Originally Posted by john4153 View Post
Consider first the switched load. If it is switched on, there is a direct path from hot to the com side. Since there is no current drawn by the voltmeter, there is no voltage drop across that load resistance.
If the com was not open wouldn't you still have an open path between the hot and the com? Why does it read 120V if its open but ~0 if it is closed.

So would there be any reason for the breaker to trip?
jsbeckton is offline  
 
Reply With Quote
Old 08-10-2010, 12:44 PM  
john4153
Junior Member
Join Date: Aug 2010
Location: Cleveland, Ohio
Posts: 13
Default

I am not sure I understand the point of confusion, but let me try to exlain.

First case: Assume the com is not open and the switched load off. Com-to-ground voltage will be real close to zero (I'll just call it zero from now on), because com is grounded.

Second case: Assume com is not open and the switched load is closed (on). Com-to-ground voltage will still be zero. Why isn't it 120 measured through the load, as happens in the case of an open com? Because, there is a load (current) and the voltage drop across that load (i.e., between hot and com) will be 120 V (Ohm's law). Com is grounded, of course, and the only reason current flows to give that voltage drop is that the grounded conductor provides a return path.

John
john4153 is offline  
 
Reply With Quote
Old 08-11-2010, 06:43 AM  
jsbeckton
Junior Member
Join Date: Aug 2010
Posts: 15
Default

Quote:
Originally Posted by john4153 View Post
I am not sure I understand the point of confusion, but let me try to exlain.

First case: Assume the com is not open and the switched load off. Com-to-ground voltage will be real close to zero (I'll just call it zero from now on), because com is grounded.

Second case: Assume com is not open and the switched load is closed (on). Com-to-ground voltage will still be zero. Why isn't it 120 measured through the load, as happens in the case of an open com? Because, there is a load (current) and the voltage drop across that load (i.e., between hot and com) will be 120 V (Ohm's law). Com is grounded, of course, and the only reason current flows to give that voltage drop is that the grounded conductor provides a return path.

John
So basically you are saying the open neutral is no longer grounded ands thus retains the voltage when the switch is closed because there can be no current flow back to the ground?

So there would be no reason for the breaker to trip if there is an open neutral?

Thanks
jsbeckton is offline  
 
Reply With Quote
Old 08-11-2010, 07:08 AM  
john4153
Junior Member
Join Date: Aug 2010
Location: Cleveland, Ohio
Posts: 13
Default

I think we are saying the same thing. John
john4153 is offline  
 
Reply With Quote
Old 08-16-2010, 06:27 PM  
triple D
Senior Member
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default o.k. here it is....

If the nail or screw had touched the hot to the neut as you earlier indicated causing some kind of 120volt anomoly on the neut, you would blow the breaker in less than a second. you would never have had the chance to even measure voltage.


__________________
See my work-Check out my album. "Git 'Er Done":D
triple D is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
recommended reading Wuzzat? General Chit-Chat 7 10-29-2012 03:59 PM
240V outlet to 120V, adapter? Finesse117 Electrical and Wiring 1 09-26-2012 02:02 PM
120v on ground wire Milwaukean Electrical and Wiring 1 12-31-2008 03:58 PM
electrical problem - 120v between neutral and ground dave0419 Electrical and Wiring 3 08-27-2007 04:53 PM