The electric cooktop at my mother-in-law's house shorted out and the new one I ordered arrived today. The stove and oven are on the same circuit, which has two 50 amp breakers clipped together. The breakers were tripped by the short, and would not re-set, so they were replaced by an electrician who said it is a 220 V circuit. Installation instructions for the cooktop say two things that sound contradictory:
1) "You must use a two-wire three conductor 208/240 VAC, 60 Hertrz electrical system."
2) "The cooktop must be installed in a circuit that does not exceed 125 VAC nominal to ground."
What am I missing?
Also, the existing cooktop is wired like this:
Stove wire House circuit wire
red to white
black to black
white to bare copper
green to bare copper
The instructions say a white neutral wire is not needed. The cable from the new cooktop has three wires: red, black and green. It looks to me like the new installation should go like this:
Stove wire House circuit wire
red to white
black to black
green to bare copper
Which seems so obvious that I hesitated to even ask it that is right, but hey, don't know much about electrical (queue Sam Cooke).
Last question: the wires from the house circuit are solid copper but substantially smaller diameter than the stranded wires from the new cooktop. There is not enough sheathing exposed in the junction box to read a wire size. How can I verify the existing wiring is adequate for the new cooktop?
1) "You must use a two-wire three conductor 208/240 VAC, 60 Hertrz electrical system."
2) "The cooktop must be installed in a circuit that does not exceed 125 VAC nominal to ground."
What am I missing?
Also, the existing cooktop is wired like this:
Stove wire House circuit wire
red to white
black to black
white to bare copper
green to bare copper
The instructions say a white neutral wire is not needed. The cable from the new cooktop has three wires: red, black and green. It looks to me like the new installation should go like this:
Stove wire House circuit wire
red to white
black to black
green to bare copper
Which seems so obvious that I hesitated to even ask it that is right, but hey, don't know much about electrical (queue Sam Cooke).
Last question: the wires from the house circuit are solid copper but substantially smaller diameter than the stranded wires from the new cooktop. There is not enough sheathing exposed in the junction box to read a wire size. How can I verify the existing wiring is adequate for the new cooktop?