I'm looking at running a circuit for a hot tub that requires 50amps. My main panel is pretty full but there is a 40amp dedicated circuit that was installed for an electric stove that isn't utilized anymore because it's been switched out to a gas stove. Here's my plan I'd like some feedback.
Run Length: 75' from main panel to hot tub. 50' of run is from main to spa panel and then from spa panel to spa it's 25'
Hot Tub Requirement:
4 wire 50 amp 220v service
PLAN:
1. Switch out 40amp breaker in the main panel to a 60amp
2. Run #6 THHN from main panel 50' out to GFCI hot tub panel with 50amp GFCI breaker
3. Run #8 from hot tub breaker to hot tub
4. The whole run is contained in 1" Sch. 80 with all joints glued.
Not sure if code requires a 120 branch circuit from the spa panel or not.
Run Length: 75' from main panel to hot tub. 50' of run is from main to spa panel and then from spa panel to spa it's 25'
Hot Tub Requirement:
4 wire 50 amp 220v service
PLAN:
1. Switch out 40amp breaker in the main panel to a 60amp
2. Run #6 THHN from main panel 50' out to GFCI hot tub panel with 50amp GFCI breaker
3. Run #8 from hot tub breaker to hot tub
4. The whole run is contained in 1" Sch. 80 with all joints glued.
Not sure if code requires a 120 branch circuit from the spa panel or not.