    An electric storage hot water tank runs on 240 volts.

    It will be wired with #10 wire, can I use 10-2/ground or do
    I need to use 10-3/ground.

    Should I use a 2-pole 30 amp. breaker, 2-pole 25 amp. breaker or a
    2-pole 20 amp. breaker.

    The individal heating elements are rated for 4500 watts and only one
    turn on a time.

    Thanks.
     
  2. Oct 29, 2010 #2

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    10/2 cable and 30 amp double pole breaker.
     