    Hi All:

    I just discovered something and am looking for help from all you electricians.

    I have a wire going from my panel to a junction box in my ceiling and no-where else.

    I decided I would use this for an extra outlet in my store. But when I went to connect the wires - Black to Black - White to White - Ground to Ground and box-- there is a thin - looks like aluminum -- flat peice of wire where the ground should be.

    Is this a proper ground?

    Any advice would be appreciated.

    Thanks
     
  2. Jul 17, 2006 #2

    iqchicken

    iqchicken

    iqchicken

    Member

    Joined:
    Jul 11, 2006
    Messages:
    10
    Likes Received:
    0
    Does the flat wire look like this ?
     
  3. Jul 17, 2006 #3

    hawkestone

    hawkestone

    hawkestone

    Member

    Joined:
    Jul 17, 2006
    Messages:
    5
    Likes Received:
    0
    No,

    It is just a flat peice of aluminum.

    It was folded over and securely clamped with the box clamp that holds the wire from being pulled out of junction box.

    The wire I should mention is the metal wrapped sort.
     
  4. Jul 17, 2006 #4

    Kerrylib

    Kerrylib

    Kerrylib

    Well-Known Member

    Joined:
    Jul 17, 2006
    Messages:
    157
    Likes Received:
    0
    Is the "wire" you're talking about, actually armored cable?

    When you look at it is it a metal spiral, with insulated wires inside?

    Sounds like the "ground" wire you are refering to is the ground inside the armor sheath. Or at the very least it is flex conduit with a ground. Even though the flex conduit is metal and conducts well, it needs a ground wire because the spiral configuration creates a high inductance (if i remember correctly). Anyway it doesn't cut it to just clamp the flex conduit to the box.
     
  5. Jul 17, 2006 #5

    hawkestone

    hawkestone

    hawkestone

    Member

    Joined:
    Jul 17, 2006
    Messages:
    5
    Likes Received:
    0
    It is armoured cable, - the outside has the spiral metal you're referring to,

    Inside it has

    • White wire
    • Black wire
    • Red Wire
    • Flat aluminum strip type thing
     
  6. Jul 17, 2006 #6

    Square Eye

    Square Eye

    Square Eye

    Well-Known Member

    Joined:
    Jan 13, 2006
    Messages:
    1,273
    Likes Received:
    10
    I noticed that you are in Canada.
    That may be something that we don't see in the lower 48.
     
  7. Jul 17, 2006 #7

    petey_racer

    petey_racer

    petey_racer

    Licensed Electrician

    Joined:
    May 22, 2006
    Messages:
    105
    Likes Received:
    0
    This is AC (BX) cable. It was/is VERY common in the states, especially in commercial settings. The AL "wire" is the bond strip. It helps keep a continuous ground path in the cable sheath.

    It is meant to be wrapped back on the sheathing before the cable is put into a connector. It is NOT a ground. It DOES NOT get terminated anywhere on any device or ground bar.
     
  8. Jul 18, 2006 #8

    Square Eye

    Square Eye

    Square Eye

    Well-Known Member

    Joined:
    Jan 13, 2006
    Messages:
    1,273
    Likes Received:
    10
    There's far more MC here than BX. MC has a green insulated grounding wire in it.
     
  9. Jul 18, 2006 #9

    hawkestone

    hawkestone

    hawkestone

    Member

    Joined:
    Jul 17, 2006
    Messages:
    5
    Likes Received:
    0
    So if it is not a ground wire,

    Where is the ground wire -- should there not be one?
     
  10. Jul 18, 2006 #10

    petey_racer

    petey_racer

    petey_racer

    Licensed Electrician

    Joined:
    May 22, 2006
    Messages:
    105
    Likes Received:
    0
    MC is a relatively new thing. By this I mean 15 or 20 years. MC is the standard these days.
    There is not much BX being used anymore. It was used widely in the past.

    The metallic spiral sheathing IS the ground. Like I said, the strip just gets wrapped around.
    Make sure all your connectors and box clamps are made up clean and tight.
     
  11. Jul 23, 2006 #11

    hawkestone

    hawkestone

    hawkestone

    Member

    Joined:
    Jul 17, 2006
    Messages:
    5
    Likes Received:
    0
    Well All,

    I made sure the thin wire looped back and is securely connected.

    I then turned on the circuit and according to my circuit tester.

    The circuit is correct.

    Thanks everyone for your help and input.
     