The electrician replaced an existing floodlight that was working well with a Wyze - I'm not happy with the Wyze one. Will check neutral bar - need to read up on that, don't know much about it. The utility guy that came out said it looked good though.Was the flood light placed on its own circuit? Or was the flood light placed on the circuit with the lights that are dimming. Be reminded that even though lights are in a different room does not mean they are on different circuits.
It is possible if the electrician did work in the breaker panel itself that maybe there may now be a loose neutral wire in the neutral bar. Even if it is not the circuit he was working with. It might not have been loose enough to cause you to see any issues until wires were moved around a bit in the panel which caused it to dislodge a bit more now causing an interruption.