Gas furnace weak flame

Discussion in 'HVAC' started by entoto, Nov 30, 2010.

Help Support House Repair Talk by donating using the link above.
  1. Nov 30, 2010 #1

    entoto

    entoto

    entoto

    New Member

    Joined:
    Nov 30, 2010
    Messages:
    1
    Likes Received:
    0
    I have Trane Gas furnace XE 60 at home and is producing a weak flame. I turned on the pilot and the flame comes but it is very weak. My house is cold ...please, please help. Somebody suggested that I adjust the screw on the pilot valve body but I don't 'see' it.
     
  2. Dec 1, 2010 #2

    paul52446m

    paul52446m

    paul52446m

    Well-Known Member

    Joined:
    Oct 7, 2010
    Messages:
    435
    Likes Received:
    1
    Are you saying the main flame is what low? if so here are some things i have found over the years. Pressure regulator in gas valve not working right,
    In coming pressure to low, Water in gas piping, water or dirt inside of gas valve,
    The grease in the old gas cock plugging off the flow of gas, out side regulator
    not passing the right gas pressure. It would be hard for you to try to adjust
    the gas pressure on the gas valve with out having a pressure tester so you can get it right. You really need a tech to check this unit out. You would be testing
    1/4 to1/2 lb of pressure so you should have a U tube to do this. later paul
     