Help with Trane Model 2TWB3030A1000A

Discussion in 'HVAC' started by MRCochran, Apr 17, 2013.

  1. Apr 17, 2013 #1

    MRCochran

    MRCochran

    MRCochran

    New Member

    Joined:
    Apr 17, 2013
    Messages:
    2
    Likes Received:
    0
    Have a Trane Model 2TWB3030A1000A. As we have had some hot days, cut it on for the first time. House was reading 80. After being outside for about an hour came in and temp was 82. Unit is blowing inside but only hot air. Checked the obvious, thermostat set at 76, it is on cool. Went outside and noticed that the fan is not blowing out there.

    Found info about checking the fan to see if it was locked up. It will spin freely, and will sometimes start with help. Shut unit down and waited two hours and turned it back on. Unit started as well as outside fan, but after about 1 minute, outside fan stops.

    Replaced capacitor as this was least expensive place to start. No change, fan will come on for about 1 minute then stops. Have checked wiring and all appear tight and no "charring" on any of the boards.

    Any other suggestions prior to calling for service?
     
  2. Apr 17, 2013 #2

    MRCochran

    MRCochran

    MRCochran

    New Member

    Joined:
    Apr 17, 2013
    Messages:
    2
    Likes Received:
    0
    Ok, I did some more checking. The unit works just fine in heat mode and runs great. When I turn it back to AC it works about 30 seconds and outside fan kicks off.
     
  3. Apr 17, 2013 #3

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,904
    Likes Received:
    3,123
    It might take a couple days but someone with some knowledge should be along soon and welcome to the site.
     
  4. Apr 18, 2013 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,758
    Likes Received:
    249
    Heat pumps are not my specialty but, sounds like it's related to the reversing mechanisms in place for A/C versus Heat.
     
  5. Apr 19, 2013 #5

    keepinitcool

    keepinitcool

    keepinitcool

    Active Member

    Joined:
    Jan 9, 2013
    Messages:
    27
    Likes Received:
    9
    So you are saying that the condenser fan will start up again after it comes to a stop if you spin it manually? And that you changed the capacitor without testing it and it didnt help the situation? Also when you change the tstat to heating mode the condenser fan works properly?
     
  6. Apr 20, 2013 #6

    keepinitcool

    keepinitcool

    keepinitcool

    Active Member

    Joined:
    Jan 9, 2013
    Messages:
    27
    Likes Received:
    9
    Anyway if that's the case it sounds like your reversing valve coil may have failed in the winter heating months. If this is the case it usually fails open which would still allow it to heat fine. Your fan may not be running because its still in heat mode, in which the fan doesn't run all the time so it doesn't pull heat from the refrigerant. That's where I would start. Hope this helps ya out.
     