Lennox 50/7.5 capacitor question

Discussion in 'HVAC' started by suzy, Jul 14, 2010.

Help Support House Repair Talk by donating using the link above.
  1. Jul 14, 2010 #1

    suzy

    suzy

    suzy

    New Member

    Joined:
    Jul 14, 2010
    Messages:
    2
    Likes Received:
    0
    Repairman replace the outside Lennox 50/7.5 capacitor with a 50/5.0 one as well as the fan motor. The old capacitor registered 4.8, is this 5.0 really enough for this unit? Repairman says it is.
     
  2. Jul 14, 2010 #2

    lloyd

    lloyd

    lloyd

    Active Member

    Joined:
    Jul 11, 2010
    Messages:
    28
    Likes Received:
    0
    Though I'd prefer to have the proper mf, It will probably work just fine. You didn't say what size unit or hp of fan you have. Sounds a little larger...4-5 ton?

    lloyd
     
  3. Jul 14, 2010 #3

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    It becomes a question of likelihoods. The guy might have gotten lucky.
    If the 7.5 had a tolerance of +/- 50%, the value can be between 3.8 uF and 11 uF 95% or 99% of the time, depending on the quality control of the capacitor manuf.

    Probably 4.8 uF does not work if his diagnosis was correct. Without looking up the Normal Distribution curve and all that
    http://en.wikipedia.org/wiki/Normal_distribution
    about 1/6th of the 5 uF caps that he picks at random will work in this application.

    When you add in that the 5 uF also has a tolerance, this 1/6th becomes less.

    He might have gotten lucky. And if that cap drifts off of 5 uF in the wrong direction it will fail sooner than one whose value is centered on 7.5 uF.

    It was probably late in the day or he was tired.




    On second thought -
    In a way, there is a contradiction here. If the design center value is 7.5 uF and he declares 4.8 uF to be unacceptably out of tolerance then he should not turn around and replace the 4.8 with a 5.0. He might as well have left the 4.8 in place.

    So my first objection was on the grounds of bad practice, and my second is that he is contradicting himself. I hope you at least got a good price.
     
    Last edited: Jul 14, 2010
  4. Jul 14, 2010 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,797
    Likes Received:
    264
    It depends on what the cap requirements for the new motor are and it could be that the old motor was still good and just had a bad cap.
    However, on most residential systems, the fan motor will come on just as soon as the compressor does so the cap requirements for the fan/compressor combination must be accounted for otherwise there's a good chance you'll burn up one or the other (fan or compressor) in the long run.
     