Need Help For Updated Heat Pump/AC Contactor

Discussion in 'HVAC' started by graybeard47, May 17, 2019.

Help Support House Repair Talk by donating:

  1. May 17, 2019 #1

    graybeard47

    graybeard47

    graybeard47

    New Member

    Joined:
    Sep 18, 2014
    Messages:
    4
    Likes Received:
    0
    I have searched the internet but not entirely comfortable on the results to order a replacement. The parts sheet for the Heat Pump on the contactor shows: CSG part# CTR-0639 with the following description: Single Pole normally open with thru bar. Contacts 240V, FLA 25.0, LRA 150.0; Coil 24V

    On the old contactor itself that has a large sticker on it: reading left to right-
    General Electric
    Volts AC 277 480 600
    Full Load Amperes 35
    Locked Rotor Amperes:
    >>1 PH (Blank)
    >> Per? ( rubbed thru)150 125 100
    Resistive Amperes Per Pole 35

    At the very bottom on the same tag: CR353CB3AH1AG

    Very small white tag near the contactor's mounting base: ;
    24v 60hz
    24v 50hz
    55-827h
     
  2. May 17, 2019 #2

    WyrTwister

    WyrTwister

    WyrTwister

    Well-Known Member

    Joined:
    May 26, 2014
    Messages:
    322
    Likes Received:
    60
    Power contactors / definate purpose contactors for condenser units are pretty generic .

    As long as the replacement contactor will phisically fit , brand is not critical .

    If the coil voltage , line voltage , amperage , is the same . If there is room to fit , I like to go up at least 1 size in amperage .

    ( Note , for HVAC , coil voltage is usually 24 VAC . )

    Wyr
    God bless
     
  3. May 18, 2019 #3

    pjones

    pjones

    pjones

    Well-Known Member

    Joined:
    Dec 13, 2018
    Messages:
    143
    Likes Received:
    50
    Location:
    Vancouver Canada BC
    Are you sure your existing contractor lists the FLA at 35? That doesn’t seem right when looking at the rest of the specs you listed for that contractor.
     