    I will be installing a whirlpool bath and it requires two 20amp circuits. The instructions say that I need to run 12 gauge black, white and green wires from the panel to the tub for each circuit. Can I use one set of white and green wires for both circuits or do I need to run six wires (3 for each circuit)?

    Jim
     
  2. May 6, 2009 #2

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,755
    Likes Received:
    249
    If your running romex, why split hairs, just pull two runs of 12/2.
     
  3. May 6, 2009 #3

    locknut

    locknut

    locknut

    Well-Known Member

    Joined:
    Apr 7, 2009
    Messages:
    75
    Likes Received:
    0
    Ignoring the instructions would prove dangerous. As kok328 said, just run two 12-2s. It's just as easy to do it right as is to "jury rig" it, and what would you save? Anyhow, the single white wire would properly have to be an 8awg. Remember that you're dealing with the high current draw of these baths.
     
  4. May 6, 2009 #4

    DaveyDIY

    DaveyDIY

    DaveyDIY

    Extreme DIY Homeowner

    Joined:
    Apr 14, 2009
    Messages:
    82
    Likes Received:
    2
    If Mfg requires it for EACH circuit, then you need to follow Mfg requirements
     
  5. May 6, 2009 #5

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    I'd be curious to see these instructions. I bet it is just a description as to how to wire it.
    I have NEVER heard of a tub requiring a completely separate 120v circuit for each function.
    There is absolutely nothing wrong with running a MWBC to these two items, unless of course the instruction really do forbid it.
    You could use a two-pole GFI breaker and not have to worry about a GFI under the tub.
     
  6. May 9, 2009 #6

    triple D

    triple D

    triple D

    Well-Known Member

    Joined:
    Jan 30, 2008
    Messages:
    296
    Likes Received:
    1
    In my neck of the woods, I put a double gang with the two gfi's in the toilet room or on a wall in the bathroom, whichever is adjacent to tub area. There are many tubs these days that require two separate circuits. These types of tubs employ a water pump and an in-line heater. Two 12-2's from panel on single pull breakers is the most efficient and cost-effective way to power this unit. Keep in mind that there are usually one or two places for a ground wire to connect to the tub, like the pump and heater. These ground lugs require a number 8 copper wire to be connected to the water line feeding the tub, in the tub enclosure. If the water lines serving the tub are plastic, there is no requirement to hook a wire to these ground lugs. Good luck...
     
  7. May 9, 2009 #7

    DaveyDIY

    DaveyDIY

    DaveyDIY

    Extreme DIY Homeowner

    Joined:
    Apr 14, 2009
    Messages:
    82
    Likes Received:
    2
    My Tub required a dedicated 20a run for the heater
    A 2nd run was needed for the pump - but it did not indicate it had to be dedicated. I also used the 2nd run for the electric radiant floor heat
    Then I have the standard 20a dedicated run for the rest of the bathroom. Lights are on another shared circuit

    If you have a MWBC - is one side of this with a shared neutral considered dedicated by code?
     
  8. May 9, 2009 #8

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    So you really think that is cheaper and easier than a MWBC???


    Just a quick clarification. This description is correct, but they are bond lugs, not ground lugs.
    I make this clarification so that a lay person does not think that these lugs have anything to do with grounding or the circuit ground.
     
  9. May 9, 2009 #9

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    A MWBC run to two separate individual loads IS considered two dedicated circuits.
     