New welder outlet wiring

Discussion in 'Electrical and Wiring' started by Bubba Ray, Dec 31, 2011.

Help Support House Repair Talk by donating:

  1. Dec 31, 2011 #1

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    My shop was wired years ago for 220 but no outlet was installed. I have black, red, white and green wires in box. The outlet called for by Miller is NEMA type 6-50 that has 3 connections with 1 marked ground. Do I just put a wire nut on the white wire and call it done? Thanks for any help.
     
  2. Dec 31, 2011 #2

    Speedbump

    Speedbump

    Speedbump

    Water well etc.

    Joined:
    Apr 17, 2009
    Messages:
    672
    Likes Received:
    72
    You need to know what these wires are or what they are connected to in the panel. White is usually neutral (not used in 230 volt applications) green is always ground and the other two should be the 230, but it's good to check first.

    What size are these wires? A welder pulls a lot of amps and I'm thinking #8 or larger.
     
  3. Dec 31, 2011 #3

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,661
    Likes Received:
    311
    You won't need the white wire as you stated. But it may not be that simple.
    What size are the wires? They should be #6 for a 50 amp line.
     
  4. Dec 31, 2011 #4

    kok328

    kok328

    kok328

    Well-Known Member

    Joined:
    Nov 20, 2007
    Messages:
    2,866
    Likes Received:
    284
    It should be as JoeD noted but, as Speedbump noted, it would be wise to verify these wires instead of taking them at face value (you just never know what someone else was thinking).
     
  5. Jan 1, 2012 #5

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    Will check wires at panel Sunday.
     
  6. Jan 18, 2012 #6

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    Wire from box to outlet is 10 gauge. I have received dif ideas on the white wire vs the ground wire to the third prong. Will not change end from welder as it is new with warranty.
     
  7. Jan 18, 2012 #7

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    24,706
    Likes Received:
    3,362
    Location:
    Chiliwack BC Canada
    Put the wire nut on the white wire and call it done.
     
  8. Jan 18, 2012 #8

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,661
    Likes Received:
    311
    The wires are too small. You can only put a 30 amp breaker on that cable.
     
  9. Jan 20, 2012 #9

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    The plug is called for by Miller but the mig uses less than 30 amps.
     
  10. Jan 20, 2012 #10

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    24,706
    Likes Received:
    3,362
    Location:
    Chiliwack BC Canada
    Change the plug to a 30 amp plug.
    The problem comes when the next owner says I can plug the kiln in there it's 50 amps and when that dosn't work he changes the breaker and burns down the house.
     
  11. Jan 21, 2012 #11

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    No way I am going to void the 3 year warranty on a new welder by changing the plug called for by the maker.
     
  12. Jan 23, 2012 #12

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    24,706
    Likes Received:
    3,362
    Location:
    Chiliwack BC Canada
    How about asking Miller what they would have you do?
     
  13. Jan 23, 2012 #13

    alaskanengineer

    alaskanengineer

    alaskanengineer

    New Member

    Joined:
    Jan 23, 2012
    Messages:
    1
    Likes Received:
    0
    To avoid both undesirable scenarios, (and assuming the welder REALLY is 30A max (sometimes welders will have a high inrush current when using posi-start or other enhanced cold-start logic)) - what do folks think of him making an extension cord with whatever plug he needs on each end - that way he doesn't have to modify his welder and when he moves out, he takes his 30A to 50A extension cord with him and the next homeowner is left with a 30A plug and a 30A breaker - this seems to be the best of both worlds. Again, disclaimer, I ask WHY did Miller put a more expensive 50A plug on a machine if it "only draws" 30A. I suspect that will be the driving concern: as it is possible that under certain settings/conditions there is a greater inrush current....
    +1 on contacting Miller about this issue - they will be able to help on multiple fronts.
     
    Last edited: Jan 23, 2012
  14. Jan 24, 2012 #14

    Bubba Ray

    Bubba Ray

    Bubba Ray

    Member

    Joined:
    Dec 19, 2009
    Messages:
    12
    Likes Received:
    0
    alaska, good ideas. I have not heard from Miller after two emails. The power numbers come from Millers specs. Why the strange plug I have no idea but it may come from the fact that this welder can work on 120 or 220 and has a plug for each.
     