Open neutral or something else?

Discussion in 'Electrical and Wiring' started by Joeb1983, May 15, 2014.

  1. May 15, 2014 #1

    Joeb1983

    Joeb1983

    Joeb1983

    Member

    Joined:
    May 15, 2014
    Messages:
    5
    Likes Received:
    1
    Last night me and the wife where whatching tv in the living room. Out of nowhere the living room started erratically cycling power about 3-4 times. (lights, ceiling fan, tv, etc.) End result being my living room is now dead...

    ALL other circuits (rooms) in my home where completly unaffected and are fine. It was only my living room experiencing the freak out.

    I went straight to the panel. Breaker was not tripped, so I cycled it which was no fix... I took my digital multimeter and I had 120v out the breaker with it closed and none with it open as it should.

    Checking a few outlets in my living room show 120v on both sides of the outlet. (hot to ground / neutral to ground)

    I replaced all the wall plates when I first bought the home and I do have the screw down connections and NOT the push-lock style. I also pulled a few plates off last nigh and did not see any loose, broken or shorted connections.

    I left the breaker off and I am at work now. When I get home I will follow the hot wire from the breaker to the bundle in the panel and see from the bundle where the nuetral is connected to the panels block. Hopefully it will be there. A quick once over last night did not show anything obvious.

    Any ideas?
     
  2. May 15, 2014 #2

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    Your voltage readings are indicating an open neutral. It could be in the panel or any one of the device boxes on the circuit. If part of the circuit is still working it could be in a working box as well. If you know the route the cabling takes the problem is in the first not working box or last working box.
    I would start by checking the box closest to the panel since cable usually run away from the panel.
     
    Last edited: May 15, 2014
  3. May 15, 2014 #3

    Joeb1983

    Joeb1983

    Joeb1983

    Member

    Joined:
    May 15, 2014
    Messages:
    5
    Likes Received:
    1
    Yeah thats what I figured. When I get home I will start at the panel and work my way down the line. Hopefully it is something simple. Appreciate the reply!
     
  4. May 15, 2014 #4

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    The loads that are plugged in in your living room are why you are reading 120v on the open neutral.
    With everything unplugged from that branch you may read 60v on the neutral with the reading depending on what kind of meter you have, the length of the branch wiring and if the cable has a ground conductor (which yours does). It's a Phantom Voltage.

    If you find an appliance that operates normally on that branch, the open in the neutral is between the living room and that appliance.
     
    CallMeVilla likes this.
  5. May 15, 2014 #5

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    He gets 120 on the neutral because a light or something is completing the loop
     
  6. May 16, 2014 #6

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Yes, the plugged-in loads are supplying the current to the multimeter. With nothing plugged in and an open neutral he should read a Phantom Voltage.

    With a heavy load like a hair dryer instead of a multimeter, it should operate between hot and ground but hardly work between neutral and ground even though the open circuit voltage on each with respect to ground is similar. It's because the source resistance of the hot lead is about a half ohm but the source resistance of the open neutral through the loads is several ohms.
     
    Last edited: May 16, 2014
  7. May 16, 2014 #7

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    I know you love your multi meter, But let's get down to solving the problem. With the breaker turned on and with a light turned on at the other end of the run. If neutral is reading 120, the opening is closer to the breaker, if it reads close to zero it is further away. That is all you really have to know and on a bad day you find a bad wire between two boxes and open a wall to find where the squirles live and chew wires.;)
     
  8. May 16, 2014 #8

    CallMeVilla

    CallMeVilla

    CallMeVilla

    Well-Known Member

    Joined:
    Feb 9, 2010
    Messages:
    1,651
    Likes Received:
    594
    Can't wait to hear how this resolves ... dead mouse in the wall?
     
    nealtw likes this.
  9. May 16, 2014 #9

    Joeb1983

    Joeb1983

    Joeb1983

    Member

    Joined:
    May 15, 2014
    Messages:
    5
    Likes Received:
    1
    Alright guys found the issue yesterday after work. I took the cover off the panel and traced the hot (black) wire from the breaker to the romex bundle at the top; then followed the neutral (white) wire back down from that bundle to the panels neutral/ground block. Sure as anyhting the neutral wire was burnt up about 3" back from the tip. I was able to simply/easily pull it out of the block. I cut the "dead" stuff off, strip and reconnected to a new terminal lug. Good to go!

    I heard the 60hz is a "slow pulse" and actually induces and slight vibration that over time will do exactly what happened... The house was built in 03. I know hospitals have a time complience/preventitive maintenance schedule to tighten them down ever so often. I did just that and tighten ALL my neutrals. To my surpise a few needed tightning.

    Learn something everday! Thanks all!
     
    Last edited: May 16, 2014
    CallMeVilla likes this.
  10. May 16, 2014 #10

    Joeb1983

    Joeb1983

    Joeb1983

    Member

    Joined:
    May 15, 2014
    Messages:
    5
    Likes Received:
    1
    Oh and every outlet on that circuit was reading 120v on both when the problem was an issue. I unlugged everything from all the outlets on that circuit as well with the same readings; although my can lights and ceiling fan are also on that circuit. All other circuits in my home read 120v on hot, 0v on neutral and 120v between the two. Now the "problem" circuit reads as it should. :beer:
     
    Last edited: May 16, 2014
  11. May 16, 2014 #11

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    So you have a loose connection that is connected until it warms up. Have you got pigtails in the boxes or are all the wires just stabbed into the back of the outlets?
     
  12. May 16, 2014 #12

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    While you were in there did you torque the other whites? If one is loose others could be.
     
  13. May 16, 2014 #13

    Joeb1983

    Joeb1983

    Joeb1983

    Member

    Joined:
    May 15, 2014
    Messages:
    5
    Likes Received:
    1
    ^ Yes sir, " I did just that and tighten ALL my neutrals. To my surpise a few needed tightning."

    ^ " I replaced all the wall plates when I first bought the home and I do have the screw down connections and NOT the push-lock style." So, all my outlets and switches are the hook/pig tail, screw down type.

    The problem was at my breaker panel itself in the garage. On each side of the inside of my panel there are neutral/grounding block terminal strips for all my homes circuits. (insert wire in the terminal block then screw down fastner) The neutral wire from that particular circuit was loose in that block causing the failure in that circuit.
     
    Last edited: May 16, 2014
  14. May 16, 2014 #14

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    Sounds good. Oldog will send you a case of beer.:rofl:
     
  15. May 16, 2014 #15

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    High contact resistance connection due to low contact pressure. Five watts may not be enough to heat up the neutral busbar at your connection but you could have had 10x this much power, up to maybe 300w.
     
    Last edited: May 16, 2014
  16. May 17, 2014 #16

    CallMeVilla

    CallMeVilla

    CallMeVilla

    Well-Known Member

    Joined:
    Feb 9, 2010
    Messages:
    1,651
    Likes Received:
    594


    This is an excellent practice ... Don't have to kill it by over-tightening, but firm retightening is a great preventative. Nicely done! :clap:
     
  17. May 26, 2014 #17

    WyrTwister

    WyrTwister

    WyrTwister

    Well-Known Member

    Joined:
    May 26, 2014
    Messages:
    142
    Likes Received:
    20
    You are very luck to have found the problem in the loadcenter . Many time , you have to spend a lot of time and effort searching for the defect . :-(

    Since you do not usually know the rout the Romex takes from the loadcenter , to device , to device , to device .....

    As I think someone stated , it is often in the last non-dead receptacle . Another problem , a home owner often forgets where all the receptacles are . And it ends up being behind the heaviest piece of furniture in the house . :-(

    More often than not , it is in a receptacle , than in a switch box or lighting box . Since receptacles often carry heavier current loads .

    Good job !

    God bless
    Wyr
     
    slownsteady likes this.
  18. May 26, 2014 #18

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    ?
    The current in a series circuit, i.e.,
    -receptacle-switch-breaker-
    is the same. :confused:

    Still, these may fail at a higher rate for other reasons, probably mechanical wear.

    BTW, IMHO, I think God damns more than He or She blesses. :(
     
    Last edited: May 26, 2014
  19. May 26, 2014 #19

    slownsteady

    slownsteady

    slownsteady

    Administrator Staff Member Admin Moderator

    Joined:
    Jun 6, 2009
    Messages:
    6,544
    Likes Received:
    1,174
    That's why we have to ask for the better choice;)
     