Underground wire break?

Discussion in 'Electrical and Wiring' started by cwlorentz, Jan 25, 2011.

  1. Jan 25, 2011 #1

    cwlorentz

    cwlorentz

    cwlorentz

    New Member

    Joined:
    Jan 25, 2011
    Messages:
    2
    Likes Received:
    0
    The flourescent lights in my garage have started flipping on and off. I checked voltage and I am only getting between 80-95 volts while this is happening. At other times I am getting 105-118. We installed a new deck and I am concerned that the underground wire to the garage was damaged. Our electric bill has gone up 75% in the last year. Can the power be bleeding into the ground and how can I tell. We have one 40 amp 220 line running to the garage that is connected to a small breaker box.

    How can I test the integrity of the 100' underground cable without digging it up.

    Thanks
     
  2. Jan 25, 2011 #2

    JoeD

    JoeD

    JoeD

    Well-Known Member

    Joined:
    Mar 16, 2006
    Messages:
    1,528
    Likes Received:
    273
    I would say a break is likely. Yes you can be bleeding power to ground.
     
  3. Jan 25, 2011 #3

    Speedbump

    Speedbump

    Speedbump

    Water well etc.

    Joined:
    Apr 17, 2009
    Messages:
    672
    Likes Received:
    72
    You could turn off all breakers in the garage, then put an amp meter on the line feeding the garage as close to the 40 amp breaker as possible. If you get a reading, it's leaking.

    You can also take the wires off the breakers at both ends and test both wires to ground with an ohm meter. Your reading should be infinity.
     
  4. Jan 26, 2011 #4

    cwlorentz

    cwlorentz

    cwlorentz

    New Member

    Joined:
    Jan 25, 2011
    Messages:
    2
    Likes Received:
    0
    Thanks for the ohm meter idea. I am not an electrician and would not have thought of such an easy way to test the wire on my own. I will disconnect breakers tomorrow and test.

    Thanks again
     