Washroom Exhaust Fan Through a Flat Roof

Discussion in 'General Home Improvement Discussion' started by cbay, Dec 6, 2010.

Help Support House Repair Talk by donating using the link above.
  1. Dec 6, 2010 #1

    cbay

    cbay

    cbay

    New Member

    Joined:
    Feb 12, 2008
    Messages:
    3
    Likes Received:
    0
    My wife and I purchaced a house built in 1970 a couple years ago. It has a low slope roof (2 in 12) with no traditional attic, but instead the Ontario Building Code Minimum of 50mm inside of an 8" joist. Insulation is limited to R20.
    The original exhaust fan didn't move much, if any, air from the washroom. Heavy condensation would always occur on the ceiling in the winter following a shower.
    I purchaced a new exhaust fan which certainly moves more air, but has created new problems. Condensation is forming within the airspace now. I have made three attempts to solve this problem.
    My first attempt was the worst attempt where I just connected the new fan to the outlet of the old, which only vented into the soffit. Of course I had probelms from this. Fans should not exhaust into the soffit.
    The second attempt I installed a proper soffit exhaust vent. My theory is that the air just returned through the vented soffit within the airflow to the ridge vent and then condensed inside the vent space.
    This last spring as part of another reno, I had the contractor install a roof vent and connect the fan to it, abandoning the soffit vent once and for all. Now we had to wait until cooler weather to see if this worked. It didn't!
    The temperature is now below freezing, and guess what? Water is once again coming through the exhaust fan.
    During the second attempt I had the entire ceiling down, the sheathing and insulation were soaked, all within 2 joist spaces to either side of the fan. Dry beyond. I am very certain this is washroom humidity causing this problem, not a roof leak. Its dry all summer.
    I am out of ideas. Please help!
     
  2. Dec 6, 2010 #2

    GBR

    GBR

    GBR

    Well-Known Member

    Joined:
    Mar 18, 2009
    Messages:
    402
    Likes Received:
    38
  3. Dec 6, 2010 #3

    cbay

    cbay

    cbay

    New Member

    Joined:
    Feb 12, 2008
    Messages:
    3
    Likes Received:
    0
    Thanks GBR. That article is very typical of what I keep running into - written assuming a full attic; though the thought that air is leaking through the fan housing is something I have thought of but haven't come up with a solution that satisfy's my desire to not add a bulkhead or drop an already low ceiling justto seal and insulate on 5 sides of the fan, and maintain the 50mm clear airspace. Is there any potential issues with through-wall venting of a bathroom? Would that work in a 4" wall?
     
  4. Dec 6, 2010 #4

    handyguys

    handyguys

    handyguys

    Well-Known Member

    Joined:
    Feb 22, 2008
    Messages:
    815
    Likes Received:
    2
    cbay - Thats exactly what I was thinking. Do a through the wall vent fan. The outside termination is less prone to leakage too. I don't like vent penetrations on low slope roofs, i'm afraid the will leak eventually.

    So, what I would do.
    Add a decent fan to the wall and vent outside.
    Remove the old fan and properly insulate the space where the fan originally was
    Remove the roof vent and patch the roof

    Down the road, consider upgrading your roof insulation. Probably from top bu building an attic on top of your original roof. This would require some engineering and carpentry skills but would give you the insulation and ventilation it sounds like you desperately need.
     