AC dims lights

Help Support House Repair Talk:

tomtheelder2020

Well-Known Member
Joined
Mar 8, 2020
Messages
197
Reaction score
73
Location
95620
Our old AC lasted nearly 30 years. When it kicked on, lights throughout the house gave a slight flicker. Our new AC also causes just a flicker but it is clearly more pronounced. Is this a problem?
 

kok328

Well-Known Member
Joined
Nov 19, 2007
Messages
3,129
Reaction score
353
Could be signs the A/C compressor is about to fail.
I'd install a "hard start" kit on it and see if that corrects the issue.
Keep in mind this would be a temp fix until you can afford to replace it.
 

tomtheelder2020

Well-Known Member
Joined
Mar 8, 2020
Messages
197
Reaction score
73
Location
95620
Could be signs the A/C compressor is about to fail.
It seems unlikely the issue is the compressor as the old unit did this for decades and the new one has done it since we first used AC about 4-5 months ago. Is there another likely possibility?
 

Eddie_T

Well-Known Member
Joined
Feb 16, 2015
Messages
708
Reaction score
483
If the lights are LED they will flicker more than incandescents. Mine flicker when the well pump cycles.
 

BuzzLOL

Well-Known Member
Joined
Oct 26, 2015
Messages
288
Reaction score
140
The flickering is just the utility transformer outside momentarily lagging as adjusting output up to match the new power consumption load as the high current consumption A/C kicks in...
 

bud16415

Fixer Upper
Staff member
Moderator
Joined
Feb 5, 2013
Messages
6,382
Reaction score
2,413
Location
Erie, PA
My thoughts are different and dimming IMO is a voltage drop problem not likely related to something outside the home if the dimming occurs when something with a high inrush current kicks on. Your service should be sized to handle such loads without a drop.



Undersized wires overloaded circuit or most likely poor connection is what I would look at.



I would start with the panel and make sure all connections both power and neutral are tightened down. I know not why but have seen over time it doesn’t hurt to snug them down.



The fact it happened the same with the old and new AC would rule out a problem with the AC. Is the AC a 240v whole house central air system or just a window unit. Do all lights in the whole house dim or just ones on the same line as the AC.

We have a large window unit that cools the whole first floor and I ran a new line from the panel to the outlet for the AC with nothing else on it. You may need to do that if it is a window unit.
 