Basement Window supporting 2 joists

Discussion in 'Framing and Foundation' started by TJ22, Dec 31, 2012.

  1. Dec 31, 2012 #1

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    My basement window is sitting on 10" concrete block. On top of the wind is a 2by treated sill plate. On top of the sill plate are 2 floor joists and there is some slight deflection in the sill plate. The joists are cantilevered to the deck. However there is nothing but the sill plate holding up the joists. The exterior cantilevered deck joists appears that they may be sitting on steel angle but its just the angle that is used to support the brick facade, I dont believe it is there to bare load. Its not a lintil that would also support the sill plate.

    I had a structural engineer in to look at it, in addition to other issues and he suggested bolting steel angle to the block. I did some quick reading and to get any type of support from that proposed solution, the angle would need to be rather large and make the window in operable.

    Any ideas?
     
  2. Dec 31, 2012 #2

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    Welcome to the site.
    Did he not requimened a size to install?
    What did he say about the angle iron outside? And how is it attached to what and has it got a bend to it?
    You said the joists outside were cantilevered, so they have no other support like a post under the other end?
    A cantilevered joist would be an inside joist that continues outside for one third of it's length with out other support.
    Is there window above this window? If there is a window above that is the same size or bigger, the header above that window will carry the weight above and you only have to worry about the weight of the floor.
     
  3. Dec 31, 2012 #3

    BridgeMan

    BridgeMan

    BridgeMan

    Well-Known Member

    Joined:
    Aug 11, 2011
    Messages:
    744
    Likes Received:
    80
    Your engineer dropped the ball by not coming up with the appropriate steel section (angle, channel, I-beam, or other) size needed to support the loads applied from above. If we knew more about the window limitations and geometry involved, we might be able to offer some meaningful suggestions.

    For sure, whatever you come up with for a strengthening member, you would to well to (gradually) raise the sagging joists and sill to eliminate the sag before bolting the new member into place. A few adjustable jack-posts would work just fine. And make a point of not damaging the integrity of the sill with your connections--meaning fabricating some short "wings" that extend horizontally from the backside of the new member onto the top of the sill, such than your attachment bolts won't split the sill.

    A few more thoughts--if there's a deck outside, why would you need to have a window that opens? Also, there's also a good chance that the cantilevered floor joists are carrying some load from a deck ledger outside. Meaning you certainly don't want to skimp on the strength of the sill reinforcement member.
     
    Last edited: Dec 31, 2012
  4. Dec 31, 2012 #4

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    If the window upper horizontal member is not bent down slightly (stretch a line to check) then the window is carrying no load. In this case the member acts as a strain gage.
     
    Last edited: Dec 31, 2012
  5. Dec 31, 2012 #5

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    I am attaching 2 photos. I think the window is about 30" wide.

    inside.jpg

    outside.jpg
     
  6. Dec 31, 2012 #6

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    If you are asking what's wrong, the simple answer is "everything".
    You might look at lowering the window and putting a header under the joists. If the framing beside the window on the inside is 2x4 going down to foundation wall you might get away with hangers for the header.
     
  7. Jan 1, 2013 #7

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    Appreciate the feedback, and I am aware "everything" is wrong. Really just looking for suggestions on what I can do to fix it. I thought about pulling the window and installing something smaller with better framing, and a host of other ideas, none of which is ideal. I was hoping to find a simpler solution, but I was unaware that the strength of steel angle at least what would fit and leave the window functional, is not that strong.

    I just realized from the photo you cannot tell but the deck does have supports (4x4 posts) outside at the end and is not a true cantilevered deck.
     
  8. Jan 1, 2013 #8

    BridgeMan

    BridgeMan

    BridgeMan

    Well-Known Member

    Joined:
    Aug 11, 2011
    Messages:
    744
    Likes Received:
    80
    Replacing the window with a shallower unit is probably your best option, allowing you to install a decent (4 x 4?) header above it, and under the existing sill plate. You could slowly jack the header into position with a small hydraulic jack, taking the "whoops" out of the sill plate. I think a slider window would be the way to go, in terms of reasonable cost, ability to open for ventilation when needed, and not looking awkward.
     
  9. Jan 1, 2013 #9

    Wuzzat?

    Wuzzat?

    Wuzzat?

    Well-Known Member Sponsor

    Joined:
    Jan 20, 2010
    Messages:
    2,471
    Likes Received:
    175
    Does your present setup cause any problems?
     
  10. Jan 2, 2013 #10

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    The present setup doesn't cause any noticeable issues. It has deflected slightly but its only noticeable if you put a straight end on it. I am more concerned for the future and since I was tackling some other issues, I figured I would address it. A smaller window with a double 2x4 header, with proper framing seems like the proper solution.
     
  11. Jan 2, 2013 #11

    AndyGump

    AndyGump

    AndyGump

    Drawer of Homes

    Joined:
    Mar 27, 2011
    Messages:
    52
    Likes Received:
    5
    Will a smaller window meet any possible emergency egress requirements?

    Andy.
     
  12. Jan 2, 2013 #12

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    Really; 4x4 header? waist of time!
     
  13. Jan 2, 2013 #13

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    What would you propose? I am open to suggestions.

    Also I just noticed in your previous post you asked about a window above this window. There is a window above this window, but ends about the mid point of this window.
     
  14. Jan 2, 2013 #14

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    The window upstairs is in the worst possible place. Each end of that header should have solid blocking all the way to the foundation.
    Now you have to look at the width of the window upstairs and how much weight is landing on that header. Is there another floor above that window. Do floor joists or ceiling joists land on that wall above that window.
     
  15. Jan 2, 2013 #15

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    The window upstairs is very large ~8' wide and ~5-6' tall. The last 1' or so of the window is above this basement window. There is no floor above that window but the ceiling joists ie roof trusses do sit on the window. They run the same direction as the floor joists. I can give you exact dimensions if that would help.
     
  16. Jan 2, 2013 #16

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    In new house construction, all headers are 2x10s doubled, anytime jack studs are landing above another header the city guys will ask for an engineers report which often ends up being a beam of some sort. In a situation like yours the beam would be built into the floor where the rim joist is and then the joists are hung off of that. If it's discovered after the fact like yours it could be worked into the wall upstairs just above the floor , spanning the window downstairs. That would take care of the weight of the wall and roof but you would still have to find some way to hang the floor joists from that beam. You might have got away with hanging the joists off the rim joists but some Half wit cut in to it.
     
  17. Jan 3, 2013 #17

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    I think I will stick a screw jack under those 2 joists and snug them up for now. Not sure how to proceed a this point. I could even take the window out entirely but the blocks beneath the window would need to go as well , as they are angled at the top.
     
  18. Jan 3, 2013 #18

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    While you think about that, the deck joists should have hangers on the other end as they are not on top of the beam.
     
  19. Jan 3, 2013 #19

    TJ22

    TJ22

    TJ22

    Member

    Joined:
    Dec 31, 2012
    Messages:
    14
    Likes Received:
    1
    Neal, thanks for the info. I actually install joist hangers on the deck joists this summer. There were just end nailed, not even toe nailed. I wish I knew what I know now back then. If I ever buy another house I will know what to look for.

    I did have an inspector look it over, however some of this was covered up so he didn't catch it. He did however catch the joist hangers.
     
  20. Jan 3, 2013 #20

    nealtw

    nealtw

    nealtw

    Contractor retired

    Joined:
    Nov 4, 2010
    Messages:
    23,900
    Likes Received:
    3,119
    So is that a single rim joist on the outside of the deck?:eek:
    Hangers and hanger nails galvinized?
     