120v on ground wire

Discussion in 'Electrical and Wiring' started by Milwaukean, Dec 31, 2008.

  1. Dec 31, 2008 #1

    Milwaukean

    Milwaukean

    Milwaukean

    New Member

    Joined:
    Dec 31, 2008
    Messages:
    1
    Likes Received:
    0
    I have a few outlets that have developed a problem in which there is not 120v present between the hot and common, but there is 120v between either the hot and ground, or the common and ground.

    Any suggestions?
     
  2. Dec 31, 2008 #2

    speedy petey

    speedy petey

    speedy petey

    Lic.Electrical Contractor

    Joined:
    Mar 15, 2006
    Messages:
    470
    Likes Received:
    44
    First off, there is no "common". It is the neutral. And the voltage is not on the ground as your title states, it is on the neutral.

    Your symptoms are classic of an open neutral on that circuit. You are reading voltage through a load connected downstream of the device you are checking.

    Turn off the circuit and check EVERY device on that circuit. If the wires are simply stuck in the back of the receptacles remove them and place them on the side screws by making the proper "J" hook on the end. The quickwire connections are notorious for failure and can create a situation just like yours.
     