Kenmore Heat Problems

Discussion in 'HVAC' started by tito, Nov 9, 2008.

  1. Nov 9, 2008 #1

    tito

    tito

    tito

    New Member

    Joined:
    Nov 9, 2008
    Messages:
    2
    Likes Received:
    0
    I am glad to have found this site!

    I have a Kenmore condensing upflow gas furnace high Eff and I can not get the gas to stay on (flame). The pilot light works. The only way I get flame is by jumping the gas vale wire with the piolt wire. This seems to only work for a little while as I imagine the pilot 25v power goes out with gas ignition on. the intermittent pilot control is a honeywell s-86 model.

    I am wondering if this is my problem or am I looking at the wrong thing. Ignition sensor was replaced last year along with blower motor and pressure switch. I figure that I am running out of parts to replace here so any help in saving me the trouble of throwing more at it would be appreciated.
     
  2. Nov 9, 2008 #2

    glennjanie

    glennjanie

    glennjanie

    Well-Known Member

    Joined:
    Mar 1, 2006
    Messages:
    2,990
    Likes Received:
    4
    Welcome Tito:
    I would look at cleaning the vent and heat exchanger tubes. Quite often the problem is a blockage in the secondary heat exchanger where the tubes are very small.
    Glenn
     
  3. Nov 9, 2008 #3

    tito

    tito

    tito

    New Member

    Joined:
    Nov 9, 2008
    Messages:
    2
    Likes Received:
    0
    Thanks, I will try that first.
     